Originally Posted by
church2k
ok. I have a dx system wit a Te5 valve in the air conditioning unit in a ship. In order to mantain the evaporating temperature positive we have installed a pm valve with the cvp pilot, so we can regulate the evaporating pressure that is going to be different that the suction pressure as its logic. the problem comes whe u try to regulate the superheating in teh evaporator. After looking the sectioning of the valve i suppose it has to be regulated until the temperature in the manometer i have already installed in the valve, will be over 5 º deg, and i have to measure the sh just before the valve respecting the 6-7 º deg upper the evaporation temperature(as u do in an usual txv).Is this correct?