Re: Freezing room problem
2.5 bar means you are evaporating at -16°C, should be more like -30, around 1 bar.
Was it working before? Air/ non condensables mixed with the refrigerant? TEV been mucked about with?
Re: Freezing room problem
True. But at 1 bar not even half of the evaporator is freezing so it doesnt even go under 0 degrees C.
There is no air or other gasses inside. I vacummed the system to -0.95 bar.
The owners says it worked before but from my point of view its kinda impossible.
I also believe that the TEV has been modified or the orrifice its too big, but it makes me wonder how it worked before.
I believe the next step is to removed the TEV check the nozzle and replace it if its too big right?
Re: Freezing room problem
You did chsrge it in liquid state i presume
Re: Freezing room problem
Perhaps the compressor isn't pumping properly. Might be worth doing a pump down test before looking at the TEV.
Re: Freezing room problem
Ok can we have some model numbers of evaporator and condensing unit,what is the delivery pressure and temperature going over the condensor please
Re: Freezing room problem
Yes i charged liquid.
I will go there again tomorrow and check compressor model, check high pressure and evaporator model( which i think i wont find since its kinda old).
Thank you for info for now. I will b
Return with more info.
Re: Freezing room problem
In an average ambient,delivery pressure should be around250 psi,do checks on the compressor pump down the liquid to see if it achieves a vacuum,
Re: Freezing room problem