here goes, the 3 wire alarm cable test continuity from ur common(orange from memory) to the other wire(purple from memory)
live from the outdoor wire 1 if sy
fit a terminal block(5amp rated) connect ur live to pump,orange alarm wire,the other alarm wire connect to 1 on the indoor unit,
N wire off pump,connect to no2 onto the indoor terminal2 wire 3 on sy connect to terminal 3 on indoor unit-this way if the pump gauze is clogging up and the pump is struggling to shift the condensate then this will stop the ac unit until the the pump shifts the water and restarts.if u run the comms line though the pump alarm circiut you will have problems. tape the terminal block up,and dyno tape a label stating that the pump failsafe stops unit-hope u understand me lingo!!