I need help with this fault code.
in fault code i find :
"More than 6 successive circuit capacity
unloads because of low suction temperature
override."
How i can change override temperature?
override."
You do not change the override temperature you resolve the cause of the fault.
Possibly -
Faulty pressure sensor, clogged
filter or low refrigerant charge.
http://eto.carrier.com/litterature/c...OL_06_2005.pdf
Page 36.
Faulty pressure sensor is ok,
clogged filter is ok
low refrigerant charge - is about 3,85.
In information menu mode is:
12, 13Low suction temperature protection (page 16)