Re: Part winding Starting
How power on windings is distributed?
50%/50% or 70%/30%
Re: Part winding Starting
My question would be, why do you want to change it?
Re: Part winding Starting
Quote:
Originally Posted by
RusBuka
How power on windings is distributed?
50%/50% or 70%/30%
Hi, RusBuka. Power rate 70/30%
Quote:
Originally Posted by
Brian_UK
My question would be, why do you want to change it?
Hi Brian_UK. Because sometime after overhauling, stator winding lead terminal mark is missing, so can not reg what (1/2/3 )or (7/8/9). So confusing
Re: Part winding Starting
Assuming that your motor terminals are not swoped around after the overhaul you have to run the winding giving you 30%power output first then 70% 2nd. that is 123 first then 789 second
Re: Part winding Starting
both of them is same PW 1 and PW2 winding in screw compressors ( betzer )and time between them is about 0.5 second
what is your compressor type?
Re: Part winding Starting
Hi if your not sure which half of winding is bigger,get a multimeter and take ohms reading the bigger half will have lower ohms reading and smaller half of winding will have higher ohms readings .So always bigger half of winding should start first ,because other wise if smaller half starts first it wont have the power to turn and it will eventually burn out.
Re: Part winding Starting
Quote:
Originally Posted by
PRESS
Assuming that your motor terminals are not swoped around after the overhaul you have to run the winding giving you 30%power output first then 70% 2nd. that is 123 first then 789 second
Thank you
But Do you agree with @GHAZ, wrote:
Quote:
Originally Posted by
GHAZ
So always bigger half of winding should start first ,because other wise if smaller half starts first it wont have the power to turn and it will eventually burn out.
Quote:
Originally Posted by
mbc
both of them is same PW 1 and PW2 winding in screw compressors ( betzer )and time between them is about 0.5 second
what is your compressor type?
Yes, that is 50/50 if PW1=PW2. my compressor is Frascold Italia, Screw type, 100Hp
Quote:
Originally Posted by
GHAZ
Hi if your not sure which half of winding is bigger,get a multimeter and take ohms reading the bigger half will have lower ohms reading and smaller half of winding will have higher ohms readings .So always bigger half of winding should start first ,because other wise if smaller half starts first it wont have the power to turn and it will eventually burn out.
Thank you.