hi to all RE eng
for a new engineer need to know more about system hunting and how to oner come it without changing machine
best regard
Printable View
hi to all RE eng
for a new engineer need to know more about system hunting and how to oner come it without changing machine
best regard
yes that is lake on system and on/off alot because flashe in liquid and it appears on txv
i need alot about it
thank you
best regards:D
If you have a leak in the system then you must fix that first, then recharge the system fully.
The flash gas is due to the shortage of refrigerant I expect and will cause hunting.
there has to be some irony here some where being where he posted this! ;)
Hi Jumanji13
Hunting should only indicate the TEV as if it were the comp or fan that would be shot cycling. So check your superheat - and probs with the valve could be SOG, Blocked strainer at inlet, Lost charge of bulb or poor contact to pipe of sensing element, or stuffed TEV. Check for basics first like touch feel for blockages on LL etc.
Ps in your next post pls give us a bit more data to go on like system parameters - press/temp/maxmin and some history if you can find and we will help as we can. BTW I will be in Cairo on Saturday, cool.
tnx alot
strainess is the proplem at all
the circuit is now clean
we will help as we can. BTW I will be in Cairo on Saturday, cool.[/quote]
thnx
nice to see you in egypt