Originally Posted by
Tycho
Allrighty!
First, a huge thanks to Josip for sending me the manual for the SAB202! (however I didn't check in here to see it before I went on site)
Ok, so I went back to the site today, repair kit for cap and Vi slide in hand. that way, I could at least open it up and look at it even if I might not need to overhaul it.
First thing, I pulled a hose up to the roof, 3 or 4 stories up and tied it down, connected it to the compressor discharge service valve and let the pressure out.
While I was relieving the pressure, I dismantled the cap indicator until I was down do the slide cover, had a smoke and did my preparations, oil absorbing pads under the cover, made ready a cut in half 5 liter container and pulled an oil drum over to act as my working table after I covered it with an oil absorbing pad and some rags. :)
had another smoke.
Removed two of the bolts holding the slide cover and put in two M12 threaded bars with extra large discs and nuts, to hold the cover in place (large discs to not chip more paint than necessary and make it look like a sloppy job (some use only a nut, but it chips the paint and scores the metal around the bolt holes and it looks like **** afterwards))
Pressure is down to 0.0 bar, but of course there will be fumes, so I don my mask, remove the last two bolts and start releasing the tension on the spring via the threaded bars.
Tension is of and I see the cap seal (U-sleave, C-ring, V-seal, or what have you, i will call it U-sleave), it looks fairly decent, no marks on it, but there are some tiny tiny metal shavings stuck in it all around as is not all that unusual, if I had not had a new one, I would have re-used it.
I pulled the complete slide valve out, which is nice to be able to do, on this, sabroe is better than howden.
Replaced the u-sleave, and accompanying o-ring, and the two "paper" strips on the end where the Vi slide interlocks with the cap slide.
Moved aside the ring holding the ball, mentioned earlier in the thread, in place and inspected the ball and the hole, seemed fine and dandy, but polished the hole with a 3m pad and cleaned it with brake cleaner then replaced the ball.
started to dismantle the Vi slide, but the ring holding the coupling cover in place made it impossible to remove the Vi cover no matter how you moved tilted it or tried to find a good angle (poor planning by Sabroe :)), and the only way to take it out would be to cut of a piece, of to take of the entire coupling on the compressor side.
So I didn't get the Vi cover off, due to time restraints and customer requests, I didn't take the Vi slide out.
Halfway consoling myself that the Cap slide seal was in good shape and that the Vi shouldn't be any worse.
So, I assembled the cap slide again and put everything in place, feeling down at heart because I didn't really find anything that was apparent out of order.
Vacuuming the compressor unit gave me time for some smokes and doing some office work on the computer before the site machinist arrived and we chatted for a while before we had 4 mBar.
started the compressor and used my permanent solenoids to calibrate the slides again.
Vi slide was off by 10%, showing 110% after having been left with the inc. solenoid on for 2 minutes after reaching 110%, corrected.
Cap slide was showing -17%, corrected and was spot on at 100%.
Switched to auto and let it run...
0.3 bar suction pressure throughout, regulated by hand on the suction valve
Vi slide starts moving from 0% to 100%, reaching 100% at the same time, the cap slide is moving.
They meet at Vi (read from the front indicator) of 2.5 and then move to Vi of 4.5 and the compressor is pulling 220 amps.
Again, I apply my dirty trick of the permanent solenoid on the inc valve of the cap slide and the amps rise and now I take it all the way to full travel of the slide, and it pulls 275 amps, the Vi slide shows 0%
So I am 5 amps below the limit at 100% slide and 0% Vi (Vi of 1.5), if I let it go down to 4.5 Vi it only pulls 210-220 amps.
I am a bit focused on the amps, since the site engineer told me that when the compressor runs like this (210-220 amps) they extend the freezing time in the freezing tunnel by 3-4 hours, and normally it would butt against the amp limit of 280 amps and work between 270-280 amps
So in my despair I go into settings and set Vi control to manual instead of auto, just to see what happens.
What happens is this, the cap slide increases to 100%, full travel (Vi of 1.5), and when we reach the setpoint, the cap slide decreases and the Vi slide follows. Noticed that both solenoids on the Vi slide are energized when it is set to manual, however, the larger surface area of the cap piston makes it push the Vi piston to 0%
A downside is that they don't get auto Vi, and during startup the Vi slide will go to 4.5, making it so that they have to be more careful during start up to not overload the compressor.
I'm completely at my wits end here...
I have THOROUGHLY read both the unisab II manual and the manual Josip sent me, and according to those, I have done everything right, but the unisab is somehow deciding that it should be running at 210-220 amps.
there have been no power outages, all the settings are still there for other things, so the unisab has not lost it's memory (don't remember if it has RAM memory that is reliant of the battery backup).
as I said, I am at my wits end...the unisab want's to be there, It didn't want to be there before, so what has changed...
Apart from normal is that the compressor has not been running for two months
"%!%%&!&%/%/(##!!!!!!!