corona inverter problem with the reactor
Hello my friends!
I have an interesting issue for you!
Yesterday I faced a common problem.I visited a corona inverter and as you can see from the photos the problem lies with the Reactor.
The corroded Reactor caused the problem.
Do you know any useful technical information about the use of Reactor?
Do you know where can I find one?
Thanks in advance!
Attachment 9962Attachment 9963Attachment 9964
[IMG]file:///C:/Users/USER/AppData/Local/Temp/enhtmlclip/ScreenClip(1).png[/IMG]
[IMG]file:///C:/Users/USER/AppData/Local/Temp/enhtmlclip/ScreenClip(1).png[/IMG]
Re: corona inverter problem with the reactor
had a mitsi 3ph power inverter with a faulty reactor- grounded- linked it out as a temporary, quoted 60quid each , quoted the customer and the tight git didn't authorise it- still running 18mth later
Re: corona inverter problem with the reactor
you tell me to remove it from the circuit,so as the a/c to work without it.
Re: corona inverter problem with the reactor
it will work without it, it just smooths out the wave form- http://www.sba.info/www_sba/images/p...g/DNE12-13.pdf
Re: corona inverter problem with the reactor
Install is correct circuit will operate without reactor.
A point to note though is the reactor limits the in rush current on power up to protect the VFD.
The added value is protection from line spikes / lightning strikes etc and to provide some harmonic filtering.
Re: corona inverter problem with the reactor
I talked with a local distributor and he told me that he has one reactor which costs 80 Euro.
What is your opinion about the price?