Charge R134 without a scale
I know that a scale can delivery a precise refrigerant charge.
However many of my students cannot afford for a scale.
I would like to improve a technique that I learnt years ago still in R12 times.
How can I charge R134 in a domestic fridge without a scale using only the manometer as a reference ?
Could anybody describe it step by step right after the vacuum step ?
Moises
Re: Charge R134 without a scale
Acrisoft, If u can mesure subcooling 5...8K I suppose it is correct. Sorry, I'm not domestic frige specialist...
easier ways i find is sweating of suction pipe with a clampmeter testing comp run amps but on a domestic you could charge on a standing pressure or and dont laugh during my junior years mothers bathroom scales they lasted bloody years but not so good on a small difference my lastest set of scales is 1 gram acuracy i think the bathroom scales depended on time of day and no battery to change
use 1kg bottles and baking scales- rated for 2kg,small,cheap,and light too.
Acrisoft
Moises
That is wrong technique and you cannot improve it.
You cannot correctly charge with manometers only. You need thermometers.
According to Danfoss service literature, you should charge to 4-7K of evaporator superheat.
http://i42.tinypic.com/34hvsph.jpg
AlexG
Charging to subcooling is only with TXV systems. Domestics are 99% cappilary tube and charging is done by superheat or by weight.
Can you afford recovery machines,do you have them ?