Originally Posted by
MazlanZ
Agree,,,,,,
Depend on capacity of NH3 capacity/volume, we also operate & maintained the ammonia refrigeration system which having about 5,000 Kg in the system.
If the volume is small, usually we dilute with air by tube /pipe it to the air suction of the condensor fans. If the volume is big, we will transfer those liquid to the skid tank or any vessels within the systems.
we are not rich enough to have the portable pump for pumping the ammonia,,,,,, we will use gravity flow tranfer or differential pressure tranfer.
mz