I can't load my copeland program for compressor info. Can someone pull the data for me on the btu's @ a 20 or 25 degree evaporator on these compressors? Thanks
kaj-0075-tac
katb-0150-cav
rs70c1-pfv-959
kaj-0075-tac
katb-0150-cav
rs70c1-pfv-959
You also need condensation temperatures. What refrigerant? What voltage, frequency, phase no.?
Check your 1st model #!
Please mention the refrigerant and evaporating / condensing temperature in F or C and frequency (50 Hz or 60 Hz).
CONDENSING TEMPERATURE IS 120 DEGREES AND THE TWO SEMI'S ARE R12 AND THE rs70c1-pfv-959 IS R-22 POT
They are all 1ph. And the kaj-0075 tac is correct.
kaj-0075-tac
TAC mean:
T=3 phase
A=Overcurent thermal protection in the terminal block
C=3 phase 60Hz 208-230V YY/Y Part Winding
"KAJ" vith TAC in model number 3 phase 208-230 60 hz could be only KAJ1 or KAJ8
Both are low temperature application models.
20°F is medium temperature application.
Check again your model number and give us right information.
For the rest:
(btu 20°F, btu25°F) condensation 120°F
katb-0150-cav (12800, 14300)
rs70c1-pfv-959 (6930, 8090)
...............................Double post!