Re: Daikin super inverter
Have you checked the temperature sensors?
Re: Daikin super inverter
Yeah I've changed the thermistors but again from the redundant unit.
Re: Daikin super inverter
Quote:
Originally Posted by
Craig Johnston
Whenever I arrive it is in a e4 fault (low pressure) when I reset the unit it works fine but the condenser freezes up very quickly.
I assume that you are in 'Heating' mode?
Re: Daikin super inverter
Yeah. It's on a biddle door curtain so the shop would kill me if I put it in cooling.
Re: Daikin super inverter
Do you have a full model number?
Re: Daikin super inverter
Re: Daikin super inverter
Tested the low pressure sensor already. Mod rzq250c7y1b biddle is UK.city m-200-dk-f
Re: Daikin super inverter
Have you checked that the Biddle unit is clean and with the correct airflow.
Re: Daikin super inverter
Yeah filters and coil clear with great airflow
Re: Daikin super inverter
What is the outdoor temperature?
Re: Daikin super inverter
On page 24 the piping diagram shows an expansion valve feeding the outdoor coil in heating mode. This may be starving your coil and causing the low pressure fault http://www.daikintech.co.uk/Data/Spl...B_Databook.pdf
Re: Daikin super inverter
Cheers Frank, thought it was the expansion valve. I'll replace it and keep you updated.