How to calculate the Flow rate of air blower(centrifugal type)
:confused:Please tell me the formula of flow rate of air blower (centrifugal type).
Nadeem
Re: How to calculate the Flow rate of air blower(centrifugal type)
Sorry, we are not manufacturers of ventilation fans here.
I suggest you ask somewhere else as this is a refrigeration forum.
There are generally two possibilities that i know. One is to measure the air velocitiy in the attached duct work. Using the formula volume flow=hydraulic area (ductwork)* measured velocity, will give you the answer. The other possibilty is to utilize the the absorbed power vs. volume flow / differential pressure chart of the fan manufacturer. Therefore you have to measure the absorbed power of the fan motor. Hope that helps.
regards
Entropie
hi all
the formula is Pt= Ps+Pv
Pressure total = Pressure staitis + pressure velocity
or
quantity= area*volume
if the duct is 2 metres by 2 metres volume is 2 metres/second
= 2x2=4 x 2m/sec= 8 cubic metres/second x that by 1000 = 8 litres a second
cool_tech
hi all
or
I think you mean velocity not volume.
8m3/s = 8000l/s
CFM = Q/1.08 x TD
Q = Total BTU or another way is this:
http://www.1728.com/flowrate.htm
His question is how much air will a centrifugal fan produce, not how to measure it in a duct.
Volume flow rate = Area of the duct X velocity
remember area = pie X diameter squared/ 4
i too have an blower...its 550 cub.mt per min, and t manufacturer says a value 60mmAq...
I am not sure as to what pressure value to be taken if I use ideal gas law to calculate mass/molar flow rate to calculate air velocity
pls suggest