Re: voltage drop on relay
I don’t quite follow what’s happening with your controller so, if what I write is obvious and you’ve already checked, my apologies! This is one of the CDC122 range of controllers? If so, the alarm relay is shown as a normally open device in the LAE literature. It is not! It is a normally closed device and if all is OK then the relay is energised and the contacts are open. If the mains supply fails, the relay contacts are closed. The alarm signal will remain and the relay remain closed, even after the fault has cleared, until one of the keys in the front panel is pressed. Does this help?
Use a solid state relay with 100-240v ac t/formed power supply. This will hold on the 180v output of the UPS and only trigger when the power fails completly. On reconnection to mains @240v the relay will reset.
would'nt a thermostat work better?
Now I dont know how fast the temperature starts rising after the power is lost tho...
Marc, that's realy a good one
Temprite, hasn't its sometimes nothing to see with the core in the relay-coil which is hanging somewhere half the coil when on 180 V, fallen/pushed not completely down by the spring. If you then trigger it back to 240 VAC, then the core is somewhat in half of it's position and there isn't enough force to overcome the spring power therefore, it stay there in it's halfway position.
Just a guess