How To Calculate PDU and Kw For Coldroom Without Software?
Hi All,
I just started to step in this industry,
Please give me some suggestion how to calculate the PDU and KW for the following coldroom.
Room Dimension: 3615mmX3615mmX4038mm(H)X75mm(T)
Temperature Require: -2'C
Storage: Chinese Broccoli/Kai Lan
Frequency To Open Sliding Door: 20% per Day.
How To Calculate The PDU and KW For this coldroom without any support of software.
Please Advice The Calculation.
Thanks a lot...
Re: How To Calculate PDU and Kw For Coldroom Without Software?
I think the product incoming temperature & its quantity is also needed here.
If you Send your email, I can send you basic calculations
smpsmp45
Thanks For Your Reply, Really Appreciate.
Kindly Send the calculation to this email add: hongyunref@hotmail.com
You will need to calculate the transmission load. Then add in the pull down load.
In Australia, if not too much pull down load, just make it 265W/m2 will do.
And you can go 240W/m2 if you want.
HVACRAU
If not too much pull down load, just make it 265W/m2 will do.
Oh, you are in Malaysia. You need allow higher, make 350W/m2 for this room...