halo, everybody, another question about which type for bitzer compressor suitable for my coldroom and the total cooling capacity calculation...thanks
sizing - length 40ft
- wide 25ft
- high 20ft
temp 0 ~ -5 degree c
Printable View
halo, everybody, another question about which type for bitzer compressor suitable for my coldroom and the total cooling capacity calculation...thanks
sizing - length 40ft
- wide 25ft
- high 20ft
temp 0 ~ -5 degree c
around 20ton of fruit & vegetable
hi
you need 48 kw compressor 6j-22.2y-40p hope it help
If you want cooling capacities, then you have to give us all the info to calculate it. It will vary from 5 till 100 kW and all answers will be correct.
hi,
Heat load calculation, need lots INPUT, as it will loading your compressor.
without this Input you are lost, As Peter_1 said...5 to 100KW...hahahah
don't forget the product SH (Specific Heat) or (latern heat) is also playing a big rules.
I trust my software.
w.l.ong
Hi,
As others said , you should give us the all details of your cold room like u said 20 tones of fruits and vegetables.Please give us other details like lighting system, on which floor it is , roof is covered or not ; everything which are the source of heat generation should be considered.