I have a friend with a small marine fridge which is on R12. Pot is gone and he has another one on R22. Question is....what changes to a cap tube length are necessary when switching over? Longer, shorter? Is there rough rule of thumb?
Printable View
I have a friend with a small marine fridge which is on R12. Pot is gone and he has another one on R22. Question is....what changes to a cap tube length are necessary when switching over? Longer, shorter? Is there rough rule of thumb?
Hi Mike
Follow this link and download Dancap http://www.danfoss.com/North_America...ils/DanCap.htm
Thanks Frank
BTW, it is really seldom that I can add rep points. What gives?
What I successfully use to find correct cappilary tube is Embraco Compressor handbook!
http://www.embraco.com/desktopmodule...vos/mp01eg.pdf
At page 65 to 71 you have capillary sizes for various Embraco compressors and various applications.
What you need to do is to find your compressor displacement and find Embraco one with same (or nearly same) displacement and application like your one!
Thanks Nike, The Danfoss one wasn't working anyway. I could change refrigerant and a couple other things but it would not spit out any data.
This calculator works well .... sometimes! ;)
http://boxload.tecumseh.com/SelectCapTube.aspx
Check your calculation with capillaries from Embraco book to see if it is plausible!
Great, another tool in the box. Thanks Nike.