Re: Toshiba r407C VRF Issue
.
407c is a complicated refrigerant because it is a blend.
If it has every had a leak and been topped up rather than having the whole charge replaced or if it is slightly short of refrigerant now then the blend can sometimes turn into a refrigerant that resembles R410A.
In both situations the result is higher discharge pressures and possibly higher running amp's.
Pulling the charge and compare the weights against the displayed weight on the unit, if it is out consider a replacement but the customer must be informed because it won't be a cheap option and no guarantee.
Rob
.