Hi guys ( and girls ?)
I have a stupid question to ask ... Is it possible to use a recovery station for charging gas in a system ?
I await your answers...
Pvl,
Well maybe, is system running or off.
It could transfer liquid quite easily, with system on or off.
What are you trying to achieve exactly , as many scenarios.
nothing in particular. I was wondering because I had a problem where I did not have enough pressure in a cylinder and system off. Does it work well and do not risk damaging the station ?
Yes its possible, i have recovered refrigerant from a system to make repairs, then reversed the process to empty the recovery cylinder back into the system. You could charge new refrigerant the same way if needed.
System repairs after recovery then system should have been evacuated, before re-charging. So dump charge back into high side. Alternatively if your recovery unit handles liquid use it to recharge repaired system in liquid phase. No short cuts.
If you recharge via your recovery unit always fit a solid core drier in the charging hose line to remove any moisture ,acid , debris etc that may be in the old refrigerant , then you know the refrigerant is in a reasonable state for the plant to work with, as you cannot be sure what condition the recovery unit is inside if it has been used on bad systems
Done it on car ac so it should work on anything
thanks for your answers
.
Recovery machines don't care which way they push the refrigerant.
From the system to the cylinder or from the cylinder to the system,
makes no difference to the machine.
Just make sure you know whether it will pump liquid, if the machine is
less than 10 years old it should be capable of handling liquid. Make sure
weigh the refrigerant and follow Glens advice above about fitting a small
dryer in the line. For the cost of the dryer it is worth fitting one.
Rob
.
Also be aware some machines cannot pump virgin gas .
I don't know of a machine that cannot pump virgin gas? and the drier is a must in both directions it will slow the process down maybe,but only by so little time you would not notice it good advice Rob.
I seen a machine few years ago that was ruined from virgin gas,It relied on the oil in the gas to help with lubrication.When pumping virgin gas it washed the bearings dry.Think the machine was a stinger and the guys were using it to decant big cylinders.Probably isnt an issue with newer machines.
I have a Refco recovery machine and it is oil free so does not harm by oil less refrigerant . But you have to be very carefull about what pressures the recovery unit can reach .
check after recovering pressure versus temperature if no non-condensables were not evacuated together with the refrigerant. Seen it many times. in that case, recharge only liquid and let some liquid in the cilinder. The liquid then acts as a seal for the air because you then leave the not wanted air in the bottle.