Good morning All.
Can someone assist please.
I have this 30gtn carrier chiller, it trips breaker immediately it wanted to start running.
I have checked all Fan Motor and Compressor for Short and they are ok.
Only one compressor is bad and I have disconnected it from the system.
All relays have been checked.
Please can someone assist me on what to do. Thanks
-
Re: 30gtn
Your Earlier posts say it all Charles.
Good day Engineers
Please I need urgent help.
I'm not that grounded in electrical.
I connected a compressor today and the result was a blast.. Breakers trip and compressor burnt.
what you are now getting I assume?
Is as a direct result of your previous actions.
Knowing when to stop is sometimes as important as knowing what to do.
Enlist the help of local more knowledgeable colleagues.
Grizzly
-
Re: 30gtn
Grizzly good pm,
Though I'm not grounded in electrical but I understand it because I read and learn everyday.
I only asked questions because I want to know more.
I was expecting someone who has experience same problem to tell me the possible causes.
-
Re: 30gtn
You've checked for shorts but have you checked the starters?
Is the supply voltage correct and strong enough?
Switch off/remove fuses to the compressors etc. Start up and recheck the starters for continuity.
-
Re: 30gtn
Get hold of Mandola's in Lagos as the local Carrier dealer they should be able to solve this problem. You seem out if your depth.
Gibbo.
-
Re: 30gtn
-
Re: 30gtn
Check that your electric supply has 3 phases.
You might have lost one when it tripped the first time.
-
Re: 30gtn
Thanks a lot Mr Brian _UK
-
Re: 30gtn
Thanks Mr Gibbo, I'm a staff of Mandilas Enterprises Limited. Carrier Division, Lagos
-