Re: R22 OPerating Pressures
Have you got a liquid line drier??It could be blocked if you`ve got liquid line temp of 44.8 and discharge temp of around 53
Re: R22 OPerating Pressures
Quote:
Originally Posted by
james770
Have you got a liquid line drier??It could be blocked if you`ve got liquid line temp of 44.8 and discharge temp of around 53
So the sub cooling is about 9K and it looks good for me.
To Futsal1st:
If you know the compressor model a cooling capacity may be estimated with the Coolpack. Check http://www.refrigeration-engineer.co...ad.php?t=16871
page end.
Re: R22 OPerating Pressures
Also, do you actually have a problem with the way the unit is performing ?
Re: R22 OPerating Pressures
Quote:
Originally Posted by
Brian_UK
Also, do you actually have a problem with the way the unit is performing ?
Not really. The plant appears to be slightly short of grunt based on continuing space complaints.
There is no liquid line drier in the system.
Re: R22 OPerating Pressures
Are you relating these complaints to your present high ambient conditions or is that not in your area?
Re: R22 OPerating Pressures
Quote:
Originally Posted by
Brian_UK
Are you relating these complaints to your present high ambient conditions or is that not in your area?
It's in my area and i am well over it!!:(:(:mad::mad:
Re: R22 OPerating Pressures
Quote:
Originally Posted by
Temprite
It's in my area and i am well over it!!:(:(:mad::mad:
I've been reading about it in our press and I must sympathize with you - geeeeez, that's hot :eek:
Re: R22 OPerating Pressures
Head seems a bit high. Is the condenser clean?
with 20C suction return and 1950Kpa head, the discharge leaving at 75C looks strangely low. I'd have expected something closer to 100C.
you write the air on temp at the condenser was about 32C so it's obviously not a high ambient problem.
I'd be taking a close look at the condition of the condenser.
on the other side of the coin, your suction pressure seems a bit low. 2C saturated suction. You say it's a TX system? Does it have a sight glass?
Re: R22 OPerating Pressures
Where did you put the compressor? Indoor or outdoor?
Re: R22 OPerating Pressures
Suct Temperature is too high and it's quite close to the evap air on temp (24), So I guess the compressor is installed outside and the suct temp is not well insulated, which makes the suct temperature incorrect.
Re: R22 OPerating Pressures
TD's on indoor unit don't look too bad. 10 deg C is reasonable. Dewpoint for 24 deg 50% RH room is not far below 14 deg so you probably don't want your supply air temp too much lower or you will have condensate issues with your supply air registers.
How's your air volume?
If you want to check if the machine is making good power, measure the air-on temp and humidity and the air-off temp and humidity of your evaporator. Get a psychometric chart and read off the values of enthalpy that correspond with these two conditions.(kJ/kg scale)
Then measure the air volume and apply these figures to the following formula:
Watts = l/s ( air volume) x (air-on (kj/kg) - air-off(kj/kg)) x 1.184
Divide the result by 1000 to get kW.
Compare this with the kW rating on the nameplate of the machine.
Re: R22 OPerating Pressures
Quote:
Originally Posted by
Futsal1st
The plant appears to be slightly short of grunt based on continuing space complaints.
I'm tempted to say the unit is running reasonably well and pumping a heavy load (cond TD 20C/36F over ambient), but given the above statement perhaps a little fine tuning is in order.
Check the superheat at the TXV bulb. Perhaps it can be tweaked a little.
Re: R22 OPerating Pressures
Quote:
Originally Posted by
wilsoncheung
Suct Temperature is too high and it's quite close to the evap air on temp (24), So I guess the compressor is installed outside and the suct temp is not well insulated, which makes the suct temperature incorrect.
The suction is a little high because the blower is running a little too fast, but as long as it doesn't cause humidity problems it is not unreasonable. A little tweak of the TXV might help balance it out.
And suction line insulation is always a good thing... if the suction line is uninsulated, this could account for a significant portion of the heavy condenser load. Unfortunately we don't have a temp reading at the TXV bulb.