TEV superheat setting and low temperatures
I am just wondering: does the TEV superheat setting change with evaporation temperature? It seems logical to me if it does, presuming that the same refrigerant is used in the thermostatic element.
Say, the TEV manufacturer adjust the TEV for 4K/7F superheat at -20C / -4F evaporation on R404a. At that moment, the additional closing force from the spring equals 0.48 bar / ~7psi vapour pressure.
Now, when evaporating at -50C, R404a, same TEV, same spring setting, that same spring induced closing force would cause the superheat setting to rise to 9.5K / 17F.
The resemblance of these calculated numbers and actual numbers of TD between SST and secondary liquid temperature, measured in my R507 liquid chiller, is scary. I always assumed that the increasing TD came from less efficient heat transfer at low temperatures, but this might be another cause.
Can somebody enlight me? Or am I just kicking in open doors, and didn't I do my homework correctly?
Re: TEV superheat setting and low temperatures
Here we all go again with TX valve superheat debate, there are many posts on the subject.
magoo
Hi Da bit.
your reporting power is 8, and you have not figured out TXV super heat yet. What the hell is going on here.
Round about now a good time for Gary and Des A and Mad Fridge and Us Iceman to chime into this post.
grump.
Are you a office bound computer tech.,?
Magoo, post is 7 years old (!!!) and one can learn more t then others in their whole life. Suggest you search once for posts of DaBit, you will be surprised.
Thanks Peter_1
really really should look at original post dating. Thanks again.