TEV with MOP: how to keep valve body temp above bulb temp?
I am using a small TEV on a liquid chiller as the metering device. This TEV (Danfoss TEN2, orifice 0X) is equipped with MOP point at 0 °C (32 °F). The TEV is feeding a coaxial heat exchanger. I chose a MOP type valve to reduce compressor overloading during pulldown.
Now, I have read in Sporlan documentation that the thermostatic element on the valve body and capillary tube must be at a higher temperature than the bulb to prevent charge migration from the bulb to the element.
What happens at my system is this: during pulldown the refrigerant starts evaporating directly after the valve needle, cooling not only the evaporator, but also the valve itself. Since coolant temperature is still high, the bulb temperature is soon higher than the valve body temperature.
Of course, this can be prevented by heating the thermostatic element on top of the valve just enough to keep it's temperature above bulb temperature under all circumstances. But what is the normal method of solving this problem?