Re: rgarding about moisture
Hello rkmoorthy,
normally dont you get high head & low back pressures when non-condensables are present?
even so, yeah you want to recover refrigerant/non-condensables replace, filter drier and then maybe tripple vac the system until 2 torr then charge to manufacturers guide lines..
Thanks,
Re: rgarding about moisture
Hello rkmoorthy,
If there are any non-condensable refrigerant charge must be replaced with a new one if the amount of refrigerant is very convenient to distill refrigerant.
for dehydration instead need to install a large capacity filter with shut-off valves for easy replacement, remember that a filter with large capacity desiccant.
regards
Re: rgarding about moisture
http://www.free-ed.net/sweethaven/Me...Num=8&modNum=3
this may help
but use a torr gauge instead of a cup of oil!
and use new refrigerant to recharge system