Did a power consumption reading on a 5 ton, single phase, A/C unit and the total power consumption for the Evap and condenser was 4.36kw. Is this reading normal?
Printable View
Did a power consumption reading on a 5 ton, single phase, A/C unit and the total power consumption for the Evap and condenser was 4.36kw. Is this reading normal?
Sorry, don't know.
What does the data plate on the unit say?
there is no refrence to the power consumption , but its a five ton single , 208 volts unit, compressor running and evap fan on high
Sounds about right - the unit is probably not running at design full load. The numbers are about where we would expect them to be with the unit running say 70 to 80% Loaded - meaning the return air and outdoor air enthalpy's are low enough to, in a combined fashion, amount to less that full design load conditions.
Waiting for a warm day to do recording of with reps from utility company using Fluke test gear. will also record ambient and room temp
single 5ton a/c , compressor running, condenser fan running, evap fan on high,
Ambient 88.5 F
Power consumption 4.352 Kw
Room Temp 71.6 F
Here's what on the nameplates.
Condensing Unit
Make : Goodman
Model : CKL60 - 1L
A/C Volts : 208/230 phase 1 Hertzs 60
Factory Charge oz R22 115
COMPRESSOR
Make : Copeland ZR57KC-PFV-250
RLA 25 A LRA 150
Evaporator
Model #UG060CKA2LACL2
SERIAL # 50050072-4118