Re: Carrier 30rba160 Chiller
Is this a single one or duty/standby config. What is the alarm code? If it is for a individual compressor circuit then check the communication bus connected to the boards, check visually for loose connection or rusted pins, Remove from the connector clean with electronics board contact cleaner spray and then re fix it.
If it is okay then may be the board is faulty, you have to replace/swap (if possible) to confirm it.
Is chiller is connected with BMS then also check the command signal.
Re: Carrier 30rba160 Chiller
You need to give the alarm code so we know exactly which comms alarm you have as there are several.
Gibbo