Refrigerant recovery with no circulating water through chiller
Hey Guys
Need to recover refrigerant charge on a water cooled chiller..Pumps can not be turned on to circulate water through the chiller while am recovering
What is the safest way or method to recover refrigerant charge with out freezing up any tubes when recovering refrigerant when there's no water circulating through the chiller.Can the push and pull method be applied to recover?
-Thanks
Re: Refrigerant recovery with no circulating water through chiller
Definitely need pumps running, hot wire water pump contactor with a jumper wire
Re: Refrigerant recovery with no circulating water through chiller
Whole system is winterized..got no water in cooling tower and no means to circulate through cooling coils
Re: Refrigerant recovery with no circulating water through chiller
if there is no water in evaporator then you can recover as normal
1 Attachment(s)
Re: Refrigerant recovery with no circulating water through chiller
Attachment 14624
Hi
might this can help you