Originally Posted by
The Viking
Short of charge? (have you measured the pipework and recalculated the total charge)
Lack of airflow across/around the outdoor unit? (Is the coil clean, the fan running flat out and nothing behind or in-front of the unit)
Is the compressor pumping properly? (This is an old lady at the end of her game, a pumpdown test will give you an indication of her efficiency)
After the above has been checked (Oh, I do assume you took a deep vacuum on her and used OFN whilst you were brazing) you need to start looking at pressure/temperature relations.
It is unlikely that it will be an electrical/control issue, they tend to either stop the unit completely or not be present...
:cool:
.