Cooling tower evaporation, blowdown, makeup and cycles
Here are the governing relationships for the makeup flow rate, the evaporation and windage losses, the draw-off rate, and the concentration cycles in an evaporative cooling tower system:
http://www.air-dispersion.com/CoolingTower.gif
M = Make-up water in gal/min
C = Circulating water in gal/min
D = Draw-off water in gal/min
E = Evaporated water in gal/min
W = Windage loss of water in gal/min
X = Concentration in ppmw (of any completely soluble salts … usually chlorides)
XM = Concentration of chlorides in make-up water (M), in ppmw
XC = Concentration of chlorides in circulating water (C), in ppmw
Cycles = Cycles of concentration = XC / XM
ppmw = parts per million by weight
A water balance around the entire system is:
M = E + D + W
Since the evaporated water (E) has no salts, a chloride balance around the system is:
M (XM) = D (XC) + W (XC) = XC (D + W)
and, therefore:
XC / XM = Cycles = M / (D + W) = M / (M – E) = 1 + {E / (D + W)}
From a simplified heat balance around the cooling tower:
(E) = (C) (delta T) (cp) / HV
where:
HV = latent heat of vaporization of water = ca. 1,000 Btu/pound
delta T = temperature difference from tower top to tower bottom, in degrees F
cp = specific heat of water = 1 Btu/pound/degree F
Windage losses (W), in the absence of manufacturer's data, may be assumed to be:
W = 0.3 to 1.0 percent of C for a natural draft cooling tower
W = 0.1 to 0.3 percent of C for an induced draft cooling tower
W = about 0.01 percent of C if the cooling tower has windage drift eliminators
Concentration cycles in industrial cooling towers usually range from 3 to 7. In some very large units, the cooling tower concentration cycles may be much higher.
(Note: Draw-off and blowdown are synonymous. Windage and drift are also synonymous.)