Headache with small bar fridge.
It is a sandwich prep table.
Problem: not cool down under 50F
machinery detail; c/u 1/3 hp, R134a, compressor: AEA4440Y, air cooled. captube system
current condition : suction side 22.5 psi, 63.8F
after condenser 210psi, 87.5F
suction sh : 38.5F, liquid line subcool: 46.6F
condenser dT: 23.7F, condenser TD: 54.8F evaporator TD: 29F
compressor out temp: 188.7F
It is really annoying me. Please help, what is wrong?
Re: Headache with small bar fridge.
confusing, post was small bar fridge that is a sandwich prep table.
Sounds similar to a sushi preparation cold bed slab.
More defined information would be helpfull.
It is a sandwich prep table + glass door merchandizer, whatever. Top portion is food stuff compartment and bottom is glass door fridge. Anyway problem is it is not working properly. I wonder evenif it is not overcharged, why subcooling is so high?. On top of the compressor is so hot, I couldn't stand 2 seconds to touch. Compressor is brand new.
High subcooling on your small commercial Capillary system is likely to be over charge BUT this won't be the only problem. Chances are your Cap tube or drier is partially blocked. Adding more refrigerant decreases condenser capacity and runs up the high side pressure, forcing refrigerant past the restriction.
Pull the charge. Vac and refill by weight. If suction pressure barely makes 5 to 10 PSI (with the same volume drier fitted as the original) You will have your answer.
Captube and drier are new ones. Blow tested with nitrogen and found strong draft thru captube. There seems no restriction exhists on capillary tube itself. Why subcool, condenser TD, compressor outlet temp are so high?
Is it possible there can be restriction in the system other than filter/drier and capillary tube?
Hello. Have you think about the possibility of non-condensable gases? But if it is no restriction in the liquid line, the LP would be higher too. It seems like you have an obstruction. IŽd check carefully the liquid line and try to measure the temp. along this line.
Vacummed enoughly. There can be no incondensible. My thinking is there seems some restriction in high side. But removing drier and captube from possibility, there is only condenser. Is it possible in the middle of the condenser exhist some restriction?
With my measured value, I found weird thing. Condenser dT was 23.7F, but Gas temp before and after condenser was - condenser in : 188.7F, out: 87.5F. That means 101.2F differance. Gas has been cooled down 101.2F passing condenser only! Is it possible in physics? Then it seems some restriction in condenser coils. But I have tested with nitrogen and found very strong blowing out thru the condenser. Anyone have experience of such a thing?
This is a typical behaviour of some restriction, so there must be one but you can't find it,
The best tool now is thermal camera that can pinpoint it.
In the past I have found that R134a systems on captube control seem to floc the oil and cause blockage in the captube.
Only solution is to replace the captube or use an alternative working fluid.
Remove refrigerant until the subcooling is 15F, then leave the system alone for at least an hour before taking new temperature and pressure readings.
Gary
Gary where have you been, good to see you back
Had a heart attack a few years back. Since then just been mostly resting on my laurels.
Gary
A lot of posts over time asking about your whereabouts & books so your knowledge is very appreciated.
Thanks. It's always nice to be appreciated. :)
As for the books, my website host merged with another company and my website got trashed in the transition. I transferred what was left of it to a new host, but never got it working. Maybe it's an omen. Time to retire.
My son in law has talked about selling the books for me... but it has yet to happen. We'll see.
Good to see you Gary, take care of that old health.:)
is it possible compressor is not sized correctly? What heat load is there? Whats the comp amp draw vs fla.
Hi, Gary.
I did as you said, this time I have renewed cap tube again and charging R134a according to subcooling. After exactly 1 hr later I've got follong figures.
suction : 9psi, 57.5F, just after filter/drier: 120psi, 83.8F
condenser in/out : 78.4/92.4f
box temp: 62f--> 55f(during 1 hour running)
sh : 53, sc : 14.2,
condenser dT : 14 , condenser TD: 19.6.
I feel box temp going down too slowly. I couldn't stay that store anymore and left.
jayryu
box temp: 16.6f --> 12.6f (during 1 hour running)
In your original post you said the box temp would not go below 50F. Now the box temp is 12.6F. Is the box a fridge or a freezer? What should the box temp be?
When the box temp is high, the superheat will be high. This is especially true on cap tube systems. Charging to subcooling will get you close, but fine tuning the charge (by superheat) can only be done when the box is very close to its design shutoff temp. When fine tuning for superheat, do not allow the subcooling to rise much above the 15F limit. I have gone as high as 20F SC on some systems.
I am sorry it was my mistake. The temp unit was celsius. That meas from 62f -->55.
Thanks Gary,
I'll try fine tuning next monday. I hope it will work really with my heart.
Given sufficient condenser airflow and normal subcooling, the condenser TD tells us about relative load. A light load will give us about 20F TD and a very heavy load will give us about 35F TD. The current TD is 19.6F, indicating light load. Given the warm box, we should be experiencing medium to heavy load. Increasing refrigerant flow/charge will increase the load.
The cap tube is borderline undersized/restrictive, but hopefully we can force a little more flow through it (by adding a little more refrigerant) without driving up the subcooling too much. Its a trade-off.
As others have said, it's good to read you again Gary.
Take good care of your health, we only get one shot.
I have heard of people rough charging warm cap tube systems to 30F cond TD with good results. I haven't tested this, but if the condenser is clean and the airflow through both coils is sufficient, this would make sense. If this results in excessive subcooling, that would indicate a restriction (or undersized cap tube). Anyone tested this?
Charged more gas and results are as follows.
suction : 14p, 54f just before captube : 145p, 88f
sh : 41, sc : 21, condenserTD: 29
box temp : 48 f , box temp doesn,t change almost at all, for 30 min. sometimes goes up or down 0.1 ~ 0.2f.
You said the cap tube was new. Is that the manufacturers recommended cap tube?
if im not mistaken that compressors design evap temp is 45 deg.
Compressor capacity diminishes as evap temp drops. A compressor that is rated at 1/3hp @ 45F would be rated lower at 35F, say 1/4hp.
Given a system that is rated at 1/3hp @ 35F, but with (in effect) a 1/4hp compressor, the compressor would be overloaded, the suction pressure would be high and the superheat would be low. Just the opposite of this system. This compressor is underloaded, not overloaded.
It is looking very much like a restricted or undersized cap tube. This being a new cap tube, I'm thinking undersized.
Regarding cap tube , it was not recommended by the manufacturer. I used supco #2 - 79" length for that application. I have field replaced captube for 1/3 hp unit about dozen times and there never has been failure of operation in my experience.
Weired thing is when I charge a captube system, I feel the temperature of hp gas on filter/drier and if I feel warm temperature on filter/drier, I stop charging. In this manner I have never failed on cap tube system. I don't trust the amount on label because it is almost always some error.
But this unit I couldn't feel the familiar warmth on the filter/drier ever.
That is the weired thing to my knowledge.
If there is a restriction in the liquid line, there will be a temperature drop at the point of restriction. That might make the drier feel cooler.
I am going to replace whole condensing unit tomorrow.
Hi Gary.
good to see you back on the forum, take care.
Shall we assume the problem has been resolved?
I have postponed to replace c/u due to the cost complained by owner. I have replaced refrigerant from R134a to R414b, and measured values as follows.
box temp : 42f
suction : 18p(23f), 46.2f, filter/drier: 165p(123.7f), 85f
condenser in air: 78.7
sh : 23.2, sc : 38.7
condenser TD : 45( seems too high)
box temp cycles 37 ~ 42f.
Thanks especially to Gary.
Seems extreme to me... and still looks restricted.