TXV query
Dear All,
I have two identical system, the only diffenece i am finding is the TXV, as
Following are the observations,
1. The Suction temp. and pressure are higher as
System #1 System #2
20°C 28°C
2. The Eva. temperature is also on the high side as
System #1 System #2
3°C 10°C
Rest all parameters are same in both the systems
Can you suggest what all possibilities are there?
Thanks
Amit Saxena
-
Re: TXV query
Very likely there is less airflow through the condenser in system #2.
What are the entering and leaving air temps on both systems?
-
Re: TXV query
Dear Mr Gary,
The entering and leaving air temps are as
System #1 System #2
Air In 42°C 42.1°C
Air Out 49.5°C 51.2°C
Thanks
Amit
-
Re: TXV query
is the heat load a bit lower in one room?