Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hi there was wondering if someone can help.......
I have been working on a nt40-511-332 box and when it gets thru to P8 on the PTI it gets down to 1.0deg C then goes back into defrost.The box then fails the PTI. I have replaced a set of defrost heaters as they were down to earth. The contrtoller software is 5146. I have had this before and it turned out to be the controller (ML2I). The refrigerant charge sees to be ok and it passes all steps up to the P8. Havent tried the P10 by itself yet, might try that but any hints or tips that anyone can give would be very much appreciated.
Has anyone had any issues with the 5146 software?
Thanks very much in advance
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hey guys i need some urgent help here.
I have a Carrier Reefer Container and just now the Controller Alarm was displaying AL60 (Defrost Termination Sensor Failure) and a while ago it completely shut down and the Controller Alarm was displaying AL61 (Heaters Failure).
But after i restart everything, it is fine up till now (fingers crossed)
Are these 2 errors code AL60 and AL61 something serious and do i need to send a technician straight away to rectify the problems?
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Dear Sir,
I have problem with my container refrigeration unit. It is carrier transicold unit model no.69NT40-511-11. When start the unit compressor is getting full frosting. Can you help me to solve this problem?
Thanks & Regards
Krish
Quote:
Originally Posted by
Will
Welcome Reefermechanic.
What ?, no StarCool ?
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Dear to all RE:
I need some advice because i will conduct a flashing. the unit is carrier although i have experience to do that but i want to have advice for some important to because the last compressor of that unit is broken so we buy a new compressor.
thank you and regards to all out there ^^:)
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Quote:
Originally Posted by
phil Landon
hi there was wondering if someone can help.......
I have been working on a nt40-511-332 box and when it gets thru to P8 on the PTI it gets down to 1.0deg C then goes back into defrost.The box then fails the PTI. I have replaced a set of defrost heaters as they were down to earth. The contrtoller software is 5146. I have had this before and it turned out to be the controller (ML2I). The refrigerant charge sees to be ok and it passes all steps up to the P8. Havent tried the P10 by itself yet, might try that but any hints or tips that anyone can give would be very much appreciated.
Has anyone had any issues with the 5146 software?
Thanks very much in advance
Hi Sir you try to replace a new DTS and HTS???
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Quote:
Originally Posted by
hzu
On a recent trip i had this problem. I was on a ship and had a carrier reefer that had a bad smv valve ( would only open 27%). I didn't have a spare on board so I took the valve apart and removed the piston as the manual said. Well while trying to adjust the temp with the suction service valve i encountered the following problem. The discharge pressure would go so high that it kept opening high pressure cutout switch. I had the suction valve almost closed then the pressure would go almost to the cutout limit and then back on and of while the temp would go down only during the period when the discharge pressure was going from high to low while average temp was going slowly up. I noticed that the quench valve kept closing and opening all the time. Now i always thought that when the smv is fully open the quench valve is suppose to remain shut. I keep wondering what did i do wrong and what was the problem.
maybe the unit is equip a STEPPER MOTOR i know 27 % in starting is ok base on my own observation ^^
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Quote:
Originally Posted by
ramakrishna
Dear Sir,
I have problem with my container refrigeration unit. It is carrier transicold unit model no.69NT40-511-11. When start the unit compressor is getting full frosting. Can you help me to solve this problem?
Thanks & Regards
Krish
Hi Krish
Some times that s normal. But some times that s not normal. Yo have to check step by step below mationed;
* You have to do P-6 SMV test, pass or fail?
* You have to check refrigerant level in the system. Maybe refrigerant level is too much??
* You have to check TXV.
If all them ok below mationed no need repair to your unit...
Good luck.
see you
Reefer mechanic.
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi reefer mechanic,
Just to ask you about SMV of reefer containers what will happen to the temperature if the SMV does not fully close while the fregiration system is running?
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Quote:
Originally Posted by
avicente
Hi reefer mechanic,
Just to ask you about SMV of reefer containers what will happen to the temperature if the SMV does not fully close while the fregiration system is running?
Hi Avicente,
When did you see SMV fully close ? SMV dosn't fully close never while the refrigeration system running. SMV does modulation cool when reefer working.
What you want learn about SMV? If SMV fully open every time while the refrigeration system running thas big problem...
Waiting your reply.
see you
reefer mechanic..
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
my dear friend,
thank you very much for the suggession. container is in transit and will do the test once it reach.
Thanks & Regards
Krish
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Alarm 60 is minor details. It will terminate the defrost on the HTT anyway. The sensor reading is wrong. Very common issue.
Quote:
Originally Posted by
nekigosu
Hey guys i need some urgent help here.
I have a Carrier Reefer Container and just now the Controller Alarm was displaying AL60 (Defrost Termination Sensor Failure) and a while ago it completely shut down and the Controller Alarm was displaying AL61 (Heaters Failure).
But after i restart everything, it is fine up till now (fingers crossed)
Are these 2 errors code AL60 and AL61 something serious and do i need to send a technician straight away to rectify the problems?
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
the 5146 software is bad.. Carrier has released 5151 now and it has repaired a few glitches. 5148 is reliable as well if you have that one around.
Can you open the controller and see if the SMV capacitor is blown? Sometimes the controller will act funny when it tries to control the SMV. Thats usually what the damage isinside the controller from my experience anyway.
Quote:
Originally Posted by
phil Landon
hi there was wondering if someone can help.......
I have been working on a nt40-511-332 box and when it gets thru to P8 on the PTI it gets down to 1.0deg C then goes back into defrost.The box then fails the PTI. I have replaced a set of defrost heaters as they were down to earth. The contrtoller software is 5146. I have had this before and it turned out to be the controller (ML2I). The refrigerant charge sees to be ok and it passes all steps up to the P8. Havent tried the P10 by itself yet, might try that but any hints or tips that anyone can give would be very much appreciated.
Has anyone had any issues with the 5146 software?
Thanks very much in advance
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi there Bruisermac, thanks for the reply, I reconfigured the controller and updated the software, still no chnage. I ended up changing the controller and that seemed to solve the problem. the box has since sailed and seems to be ok.
cheers
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hi to all reefer technician and pleasant day to all...
i want advice from the other techncian who's have a long experience in daikin reefer van
i wonder what is the common problem of daikin reefer van the compressor is hermetic,....and what is the most important to check up always after PTI
thank you and take care ^^
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hi to all reefers technicians and good day to all
i have a big probleme with carrier but rearly i need solution .
the probleme is ice in he pannel reefers alwys reefer is out of range.
i make defrost ,wather in the evap .but same probleme.
best regard
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi guys,
1st time here. got an alarm E109 on Daikin unit LXE10E-A1. ANY SUGGESTIONS? I regularly working on TK, Carrier and Mitsubishi but not Daikin. Any help is highly appreciated.
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Quote:
Originally Posted by
heaviw8
Hi guys,
1st time here. got an alarm E109 on Daikin unit LXE10E-A1. ANY SUGGESTIONS? I regularly working on TK, Carrier and Mitsubishi but not Daikin. Any help is highly appreciated.
hi heaviw8
i was send e-mail to your e-mail adress. Have you check it?? Whats happen, problem solved??
see you
reefermechanic
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hi to all reefers technicians and good day to all
i have a big probleme with carrier but rearly i need solution .
the probleme is ice in the pannel of supply alwys the reefer is out of range.
best regard
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
wrong litium battery into controler. Replace battery and softweare.
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Quote:
Originally Posted by
obet
hi, all power relay replace with new one and the keypad we put also new one but the same problem " emergency program"
wrong litium battery into controler. Replace battery and softweare.
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hhhhhhhhhmmmmmmmmfffffffffff
a good day to all of us reefer technician :(
i have a problem in my daikin FAILURE of RETURN SENSOR alarm although the unit is running i can't see the display monitoring of RETURN in reefer i want to replace the sensor but i can't find any dealer here in my country so what can i do now???can i use the sensor from the partlow???so can i use again the unit while im waiting to have a brand new return sensor???
thank u :(
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hhhhhhhhhhmmmmmmmmffffffff
hi mr.reefer mechanic i want to ask something because i have new overhaul compressor so i installed in my unit all the system is clean i use nitro and r-141 and i vacuum the system and then i replace a new filter dryer, i operate the unit, after 30mins i see a abnormal movement of my oil compressor because i see in the sight glass that will become empty so no oil come back in my crankcase right???!!so maybe i have a defective TEV may i right??? pls help me :(
thank you so much
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
HI There,
I am reefer man from malaysia, i hope to share information with all reefer engineer, technician,mechanic
Rgds:D
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Quote:
Originally Posted by
kheilan
hhhhhhhhhmmmmmmmmfffffffffff
a good day to all of us reefer technician :(
i have a problem in my daikin FAILURE of RETURN SENSOR alarm although the unit is running i can't see the display monitoring of RETURN in reefer i want to replace the sensor but i can't find any dealer here in my country so what can i do now???can i use the sensor from the partlow???so can i use again the unit while im waiting to have a brand new return sensor???
thank u :(
Dear Kheilan,
is in return display E
.ON Chartls & Calibrate the partlow chart.
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hi reefer mechanic how r u
can u help me i need daikin and thermo king service manual where i will get these both are if u have plz sent as a pdf this my id animon.2008@rediff.com
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Quote:
Originally Posted by
REEFER CONTR
Dear Kheilan,
is in return display E
.ON Chartls & Calibrate the partlow chart.
thank's for the info. i replace a new sensor for return. cheer up :D
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
a good day to all reefer technician.....can i ask a few question... . . . . :Di have new overhaul compressor because the past history of the compressor is broken piston so we overhaul the compressor and now, the compressor is ok i decided to use in reefer CARRIER ML2 now i have seen the abnormality of compressor because before i start using the unit i have been charge the OIL 3/4 of sight glass and now after 1hr and half the oil is running out, so i shut off the unit and start thinking what is the possible cause of that.... .. . . .now i don't have any idea what is going on this is the first time i encounter a problem like this.... .. .-5c before i shut down, the company of compressor repair said to me that my TXV is defective is this possible cause??help me :((tnx
-
1 Attachment(s)
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
dear sirs
i am not a reefer technician but my situation warrants an immediate solution so i seek your professional help. Attachment 7949
we have done initial precooling to -20C before loading the -18C products. however after 20 hrs of cooling only -9C was reached, compressor covered in ice and sight glass white with bubbles. shud i unload and return to the cold stores? kindly advise
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Request Service Manual mitsubishi daikin.
thx
mcnc6@msn.com
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Quote:
Originally Posted by
fercmal2
dear sirs
i am not a reefer technician but my situation warrants an immediate solution so i seek your professional help.
Attachment 7949
we have done initial precooling to -20C before loading the -18C products. however after 20 hrs of cooling only -9C was reached, compressor covered in ice and sight glass white with bubbles. shud i unload and return to the cold stores? kindly advise
Hi fercmal
without any technical info, I would suspect you either have a dirty/blocked evaporator coil or an evaporator fan is not running
R's chillerman
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hi chillerman
thank you very much for the reply. may i ask what technical info do i need to resolve this prob.
on another note, when loading to a reefer van, which is better
1. precool to setpoint (-20C), turn off unit, then immediately load frozen(-18C) products at ambient temp or
2. precool to setpoint, turn off unit, open doors and allow container to reach ambient, ensure all water(condensate) inside container is evaporated before loading frozen products
sorry for taking so much of your time
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi fercmal
with loading pull to temp and then load
with the container unit, they normally have access panels to evap/fan on the outside
you can (carefully) check if all fans are running through them, and after a defrost you
can turn the unit off, dissconnect power supply plug and get your head right in there with a torch
to check evap, has defrosted or not, if not you may have heater bars gone down
depends on your electrical knowledge on if you can change these yourself or not
as they are multi-speed, multi-voltage, so have quite a few wires on fans
I presume you have transfered the load now, so in the back you can remove the large panels
to gain full access, Problem if fan not running though could be a contactor fault or control circuit & same with heater bars
So your probaly need an engineer to diagnose/rectify either way
R's chillerman
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Quote:
Originally Posted by
fercmal2
dear sirs
i am not a reefer technician but my situation warrants an immediate solution so i seek your professional help.
Attachment 7949
we have done initial precooling to -20C before loading the -18C products. however after 20 hrs of cooling only -9C was reached, compressor covered in ice and sight glass white with bubbles. shud i unload and return to the cold stores? kindly advise
Hi Sir,
You have to check the electronc expansion valve. And also there is too much refrigeration in the system. Check alll them.. Good luck.
see you
reefer mechanic
-
1 Attachment(s)
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Attachment 8271
Dear All, For Your Information
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
MSG FROM colleagues
We bring to everyone attention below important message concerning the explosion of container refrigeration units due to suspected wrong refrigerant gas top up during servicing of the units. The explosion occurred from the compressor when units were conducting PTI (Pre-Trip Inspection) and it has resulted 3 casualties unfortunately.
Based on our latest findings, 4 reefer units have exploded; ie 3 from Maersk (2 in Vietnam and 1 in Itajaí, Brazil) and 1 from CMA (in Qingdao, China).
Two units were exploded on 27th April 2011 and 28th April, 2011 in Vietnam; another Maersk unit was exploded on 7th October, 2011 in Brazil; one CMA unit was exploded on 9th October,2011 in Qingdao. Fortunately the exploded unit in Qingdao has not resulted any casualty.
We also share below attached reports and quote from our China/Brazil office.
=Quote on Oct 14 from MOLBR =
We received an incident report fm our TAO reefer vendor, a compressor had exploded on a reefer unit when it was being plugged in for PTI at their depot facility. The intense of the exploded compressor had ripped off the entire machinery compartment right into the front access panel of the container. Fortunately at time of the explosion, no technician was attending to the unit as otherwise it would be fatal.
This reefer unit was mty repo fm Vietnam to TAO and it was being reported that there were 4 similar cases happened recently at other locations which the reefers were also exported fm Vietnam. The cause of the compressor explosion is still under investigation by China Classification Society but may be due to abnormal pressure built up in the compressor caused by non-conformance ***** gas being charged into the system.
In this regards, could you kindly inform and warn all depot reefer vendors to take safety precaution, to check the pressure on both the discharge and service valve, esp for unit that is mty returned fm Vietnam and if deem necessary to flush out the ***** in the system and clean it out completely.
Attached file herewith, aftermath photos on the extent of the damages sustained on subj reefer taken at TAO for your reference.
=unquote=
Feedback from our Brazil reefer vendors indicated that Vietnam reefer vendors might have injected GRP and L12 gas instead of R134. Maersk has since postponed its PTI arrangement in Brazil on the 300 units loaded from Vietnam during March to May period.
HKHKGLEM has also followed up with MOL Vietnam to further understood the case. The 2 Maersk units exploded in Vietnam happened on April 2011 and the vendor was APM Saigonship (A joint venture company with one of Maersk’s subsidiary). Preliminary findings indicated that APM Saigonship might have injected wrong refrigerant into the reefer units during reefer servicing. On the other hand, MOL Vietnam confirmed the current 5 reefer servicing vendors appointed in Vietnam (3 in HCM, 1 in HPH and 1 in Danang) are using R134 refrigerants that origins & manufacturers are Dupont (USA), Klear (Japan), Forane (France), Kalton (Germany) and Forane (France) respectively. As a safety precaution, MOL Vietnam will also generate the reefer lists being serviced from March period. These will be shared on next distribution.
Separately, HKHKGLEM gathered H. Yamamoto san of JPTYOLEQ comments that the explosion might be due to HC-12A ***** (a flammable refrigerant) wrongly injected to R134A base reefer. He is currently gathering information from Carrier Transicold to confirm it.
HKGLEM will continue to follow up with Vietnam and respective offices involved on the development of this case. Should you have any updates to share, please forward to HKHKGLEM for consolidation and distribution. We would like to streamline all updates on this case vie HKHKGLEM. During the interim, we would like all offices to check from StarNet system on units origin before PTI. If in doubt, please do not hesitate to contact HKGLEM.
Please also distribute this information within and to all related parties.
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Quote:
Originally Posted by
reefermechanic
...................
reefer mechanic
Hi Sir:
I work in field SBII thermo king, and i have some problems in cycle senetry switch. could you please to send me anything related in like diagrams, wiring code and possibe cause .....
Any help is appreciated.
thanks alot
My email is giath2008@hotmail.com
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi Reefer Mechanic,
I am working on a Daikin RZP125DV1 and the customer gets Installation Manual but not the Service Manual.
Could you help me with that issue ?
(After changing indoor unit, the Daikin does not start and gives E4 error code).
Thank You
Alain
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hello im here again and again :D i need a advice because im working now on my CARRIER REEFER CONTAINER VAN here my trouble i have a unit thus have alarm 20 fuse blown so i check the control box and i see the 10ampere fuse blown so on the spot i replace a new and good 10ampere fuse now i can clear the alarm 21 to the unit, i thought the unit is becoming ok if i replace that fuse but when i try to start the unit when the compressor is running or contactor compressor is running the fuse 3 is blown again and again and again.
what is maybe the possible problem of this unit any idea or experiencing this trouble kindly share to me thank you so much.
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Quote:
Originally Posted by
kheilan
hello im here again and again :D i need a advice because im working now on my CARRIER REEFER CONTAINER VAN here my trouble i have a unit thus have alarm 21 fuse blown so i check the control box and i see the 10ampere fuse blown so on the spot i replace a new and good 10ampere fuse now i can clear the alarm 21 to the unit, i thought the unit is becoming ok if i replace that fuse but when i try to start the unit when the compressor is running or contactor compressor is running the fuse 3 is blown again and again and again.
what is maybe the possible problem of this unit any idea or experiencing this trouble kindly share to me thank you so much.
Hi khelian,
check your mail box
see you..
reefer mechanic
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Quote:
Originally Posted by
mimini
Hi Reefer Mechanic,
I am working on a Daikin RZP125DV1 and the customer gets Installation Manual but not the Service Manual.
Could you help me with that issue ?
(After changing indoor unit, the Daikin does not start and gives E4 error code).
Thank You
Alain
Hi Alain,
I think your unit is not refrigerated container unit. I cant help you. sorry..
see you
reefer mechanic