Re: Frequent compressor cycling when using a ASHP for shower water heating alone
The typical low flow showerhead is 7-10L/min
The only advantage I see to parallel flow is more reliable water pressure at the showerheads. Series flow would give more reliable water temperature at the showerheads.
How do you achieve high efficiency with a heat pump. "keeping the discharge pressure low for as long as possible"
How do you achieve this in a thermal storage system, By heating a store of cold water.
Start from the beginning cold tanks), tanks and H/E in parallel. The heat is introduced into the tanks, natural stratification will cause the heat to rise to the top. Discharge pressures will remain low, slowly increasing over time.
When the tanks reach set point half way up, most of the mass of water in the tank will be close to the set point temperature. Units turns off. So good so far?
Right, somebody a has a small shower, will effect the control thermostat or the temp at the top of the tanks 'NO".
The use age increases, until about the half the tanks are now full of cold water. (the top is still hot) The heat pumps thinks it is heating cold water, so discharge pressures are low rising after time.
OK I do not like buffers or internal heat ex changers for this application.
I suspect that the reason for the the 2 pumps is the unknown pressure drops through the cylinder heat ex changers.
@ MikeHolm: regarding the specification of the 300L tank, i have no clue, and finding out will be practically impossible. Nevertheless, the design of this firm (named "Ideal" :-) should probably mimic the design of Israel's most valued off-the-shelf water tanks - Chromagen - located in Kibutz not far from Armageddon. For a specification of their tanks, take a look in their single spiral 300L tank in this document on pp. 32. The inlets & outlets are of course differently positioned, but the tube specification should be similar. The supplier did tell me, howerver, that the spiral heat exchanger is 12[meter] long. I am impressed by your knowledge of the local codex. In case i am not mistaken, for ~30y now, it is obligatory to install, in buildings up to 9 stories high, a public solar system backed up by electric heaters. each appartment has a small tank with a spiral heat exchanger, which is fed by solar heated water. each tank also has electric heating backup. Generally speaking, basic passive solar water heating is THE most efficient and cost effective way to boil water in Israel. Unfortunately, this building was built 31 year ago, and the contractor chose another heating option - a central diesel water heating system. Since the penthouses in this building occupy most of the roof area, we are only left with 15[m^2] of public roof, and after seriously considering a pure solar system, it was dropped due to bureaucratic reasons way-way-off this topic. Actually, i made an exhaustive economical reserch regarding the available heating alternatives: I calculated the net present value of each option, taking into account even the rate of accumulation of scale, and the resulting degradation this inflicts on the electric and solar systems. @Gary: I think that having to do with alternative energy resources is good for your health. Take, Zvi Taborr, for example (a native English speaker as well). This kid is only 94 year old, and his mind is crystal clear.
@ Mad Fridge:
when only a single pump was installed the compressor cycled more than 100[times]/24[hr].
increasing deltaT from 6 to 8°C dropped this to ~70[times]/24[hr].
installing a seconf water pump resulted in a fruthe decrease to ~30[times]/24[hr].
Had a look at your cylinders, as normal short of surface area for heat pump applications (the coils are not big enough) But they are at the bottom which is good.
Measure the temperature coming out of the cylinders (feed to the showers)
around the world designers are using boiler or solar systems for heat pump applications, and these methods are incorrect.
If you want 50C in the storage cylinders, then really you need at 60C feeding the internal heat exchangers.
The efficiency of a heat pump is determined by the temperature/flow of the water entering the heat pump heating side, colder the water/higher the flow the more efficient.
The short cycling is an effect, not a cause. I could just tell you to reduce your cycling, but that would just be another mask, not fixing the problem.
Even though I have given you a drawing, this for your application and cheap to fix, this is not what i would design from new.
I am following this closely here, learning plenty, am definately going to make sure I order a 'mad fridgie' from my suppliers this week and stick a mini you in my toolbox, to make all I dont quite understand fall into place.... and am really looking forward to our pint and seeing your new 'Heat Pump' release for the uk....Top Man MF & thanks for looking at this for Yonatanb
R's chillerman
mad fridgie
I would assume that series tanks with stratification would be more effective at separation of water temperatures than parallel tanks with stratification, and therefore provide colder water to the heat pump for a longer period of time... on the other hand, I assume you have tested both strategies and found the opposite to be true?
Apologies Gary, if that read odd, I was not glossing over your expertise in just about everything....I just thanking 'Mad' for taking the time to look at this for yonatanb as per the message I sent him the other day
R's chillerman
[Jedi hand gesture]
These are not the droids you are looking for. Gary is an expert at just about everything. Move along.
[/Jedi hand gesture]
Gary, it about the water flow through the heat pump and control of the water in the storage cylinders.
On a one pass system (where water leaving the heat pump at a very high temp) then you are correct, however very high outlet temps mean permanent high discharge pressures, and lower efficiency. How ever if you for a full circulation system, where the heat pump only increase the temp of the flow by a few degree's per pass, the discharge pressure are kept low for longer periods. (only at the end is the discharge pressure high) for this to cylinder heat ex-changers must always bee in the coldest part of the system (I do not use internal heat ex-changers, I pump from the cylinder through a heat ex-changer and back again returned at low level)
It is all down to flow, heat transfer and available duties. You have to look at the whole application and the influences of each part of the system. What is installed is a boiler system!
yonatanb
Yonatanb,
I am familiar with codes in a few countries and I do a lot of solar so Israel was always a model for us in North America, to no avail, as it is not mandated in any code here. I know the Chromagen product and the HX is in the bottom 2/3 of the tank.
I assume the fittings are 3/4" or equivalent so there is not much HX area in one tank. The pressure drop is too high for all three in series and the usefullness of the last tank is suspect. Put them in parallel. You will have a huge increase in performance. The HX is only 1.2m2 per tank which would be good for about 6kw each when the dT is 20C. I don't think you can get the performance from the tanks with such a small dT. You need to get a higher flow through each HX and with the current arrangement you will not get much more.
Mad is right, as this system is similar to a solar system except the dT is a lot smaller than we would have with solar. The tanks were designed for solar.
MikeHolm
The pressure drop is too high for all three in series...
Okay... I'll buy that explanation. If this is the case, then parallel would indeed be better than series.
Three in series gives you resistance times three. Three in parallel gives you resistance divided by three, which means much more flow.
I'm going to bed....Long day today
A long read. Can someone summarise why, with dedicated circulation pumps, the heatpump thermostat keeps telling the unit to re-engage, in such short time intervals?
Where is the temp probe actually measuring at the moment?
Where is the OP going to move it (temp probe) in future developments?
Gary
The 7 liter figure is from memory... maybe it was 27... or maybe something entirely different... I'm old, you know... they say the second thing to go is the memory... I forget what the first thing was.
Depending of shower head and pressure water consumption could be 5-7 or 3,5 or 2,5 galon per minute of showering.
From my memory, here in Europe we use design figure of about 70l per shower.
http://i51.tinypic.com/2i9gqx.jpg
This pipe and electrical heater setup on improvised stand is looking strange to me, and it looks more like this tank should be mounted horizontally.
Could OP give more details of make and model of this tanks?
@ desA:
The heatpump operation is triggered by an internal sensor at the output of the heatpump. All the readings I previously provided are taken from this output sensor. I can also monitor the temperature in the inlet of the heatpump if required.
The local expert does not rule out any of your suggestions, but he would like to follow his debugging procedure, which includes replacing the two water pumps with a single centrifugal water pump.
after the problem is solved, one way or the other, i will summarize everything, and post the the summary so all of the experts here could draw final conclusions.
@nike123:
Thank you for your comments !
you are correct. the labels on the tanks indicate both horizontal and vertical operation is possible.
70L of hot water per shower/bath is a gross exaggeration in a country where 10,800,000 inhabitants occupy ~28,000 [km^2], most of which is defined as a desert (==annual precipitation is less than 200mm). the government here has actually installed water savers on each faucet (either in shower or in the kitchen). anyways, taking short showers is part of the basic training here.
yonatanb
@ desA:
Can you provide further information of exactly how & where this sensor is located, on the heat-pump internal pipework? A few pictures would be great.
In my view, this is in all likelihood the root of your difficulties. We should clear this difficulty first.
Any detail on manufacture of tanks and model of tanks?
@nike123:
nothing more than the details specified in reply to an earlier comment by MikeHolm.
@desA:
The sensors are hidden under the hood, which i do not want to take off due to warranty issues. In case my cyber presence is tolerable, i promise to update this forum with any development.
This is what is going to happen! New pump "all Ok now mate"
What is really going to happen, increase set off set point, increase differential (lowers "cut in" point) increase anti-cycle timer just in case. No short cycling now.
The facts are!
Not enough surface area in your cylinders (regardless of the configuration)
DesA is an expert on heat transfer, what would you expect the entering water temp to be, passing through 1" 12m long spiral tube inside a static cylinder, if the water in the cylinder is 45C to deliver 6kw of energy?
@mad fridgie:
you are my guardian angle! i will closely monitor all the parameters you have kindly provided. additionaly, i will closely monitor the CoP.
other than that, the heat exchanger spiral in each tank is 12[m] (about 40 ft.) long, not 1.2[m].
I see 3 pipes are comming at bottom of cylinder and 1 pipe at side of tank. One connection is blanked.
Middle tank have side outputs which are different in position than other two.
I think we should first confirm that tanks are connected as it should be regarding inlets and outlets.
I think that parallel tanks configuration is better one, but it must be balanced.
Since heat pump works with temperature difference of 5K to 8K at maximum, heat exchanger surface of tank which is made for 10K (or more) differential is to small to transfer effectively heat to water in tank and therefore you experience frequent compressor starts and short running time.
In paralel (balanced) setup, same energy is disipated from 3 times bigger surface and you should have better heat transfer to water in tanks and your heat pump temperature diferential should drop to 5K.
Could you take picture clearly of labels on tanks and translate to english what is written there?
Below "Ideal" what is written on Hebrew?
yonatanb
@ desA:
@nike123:
In Toronto, We have set up hot water meters on 100 houses as a test to see what the average shower length is and how much water was used with different shower heads and under pressures which vary from 3-4bar (typical for Toronto). From my own experience, my normal 5min shower is using 25-28L but I am not a teenage kid and don't do 30min showers. The range in the 100 houses was from 20-80L so it is hard to get a concise figure.
We are also heating from 5-8C to 50C typical.
yonatanb
@mad fridgie:
I think if you look at the spec of the HX the coil is 1.2m2 of SURFACE area not length of tubing....and surface area determines heat transfer in this case.
Also, by looking of how is piping done and stands for tanks, that is some "hack of the year".
@MikeHolm:
i think Mad Fridgie referred to the length, and i gave the figure i was handed by the installer. you are right of course regarding the Chromagem tank spec. and regarding the postulates of physics.
instead of feeding you with partial/incorrect/irrelevant data, i contacted the tank supplier for details, and hopefully, he will send me some kind of a spec sheet with actual drawings. since most of the suppliers here religiously believe in the "buy & go (to hell)" principle, i can only hope for a miracle (isn't the holy land a fine place to do so ? :-).
@nike123:
A. by "piping" you refer to the design or the physical connections?
B. what is wrong with the stands and how does it affect the system's performance?
i will call it a day. thank you again!
yonatanb
Nope. I refer to layout of pipes, not design. This is not the work of professional.
This is work of "take money and run fast and far as possible" "professional".
It does not affect system performance, but it tells lot of "professional" who even doesn't have will, time, money or whatever, to paint them at least in primer.
yonatanb
For my part, I have come around to Mad's way of thinking and feel he has the best solution.
mad fridgie
Mads way of piping is fine, just remember to have the "header pipe" at least one size larger than the pipes from the tanks. In this way, the pressure on each tee going to each tank will be equal and you will get equal flow through the tanks. This applies to both the DHW piping and the HP piping.
yonatanb
@desA:
Until you can accurately answer this question, I fear that further discussion will be pure speculation. :confused:
You may want to ask the machine supplier/builder for further details.
Firstly apologies, the heat exchangers are indeed 1.2 square meters!
I have re-read the thread.
Water use 700L form say 20C water in to max water out 55C, 28.5kwkr/24hrs
That is about 25L/person (remember that the hot is mixed with cold to give the shower head flow) and that would seem about right.
You will have losses from cylinders (2kw per cylinder) total 6kwhr/24hrs.
So the max amount of heat required is roughly 34.5kwhrs/24hrs.
Power used is 17kwhrs/24hrs that a COP of 2, and that is shocking especially in the ambient temperature range.
It is very clear that the installer has no clue what he/they are doing. (well they know how to make a bob or 2)
So the fix and some money back!
A; get them to rip it out completely and get a full refund (unlikely to happen)
B; Re plumb the cylinders as shown "in parallel", ( I would normally get rid of the buffer tank, but as they have no clue best leave in as a low loss header, leaving in 2 pumps one for heat pump and one for the cylinders), replace the whopping big 18Kw unit, and replace it with a 3-5Kw heat pump unit. Control the heat pump directly or indirectly by the storage cylinders temperature (sensor 1/2 way up the cylinder). turning off the water pumps when heat pump is not in operation.
You require at least 0.5l/s going through the heat pump, and at least 0.5L/s going through each cylinder heat ex-changer (1.5L/s total)
I would have the cylinder stat set at low 50Cs cut out, and 40C cut in. The internals of the heat pump cut out as safety at 58C (return water temp).
This will give a reasonable balance between heat pump, heat exchangers, use and give you great COPs ( i would expect the COP to between 4 and 5, or power usage around 7-9kwhrs/day)
"Then ask for a refund on the price difference between the units"
PS: I do not agree with coils in cylinders for heat pump applications!
Mad, the problem here is that, even if the system is piped perfectly, I fear that the total HX area is less than half than it should be for the desired heat transfer. You will not get the same heat transfer from an immersion coil that you will get with a system pumped both sides.
That said, if the OP used 3 Viessmann tanks with 2.0m2 surface area, piped correctly, the performance would be drastically different. The problem lies in that with the small deltaT, each of the current HX is good for, I think, at best 4kw so with 18kw to play with...............................ain't gonna happen.
Yonatanb, ask Mad to draw you a diagram with an external HX and I will look at the tank drawing to see if we can use the existing ports on the tanks to pipe it in. In this way we may be able to give a much better performance.
MikeHolm
Hi Mike, I agree (read my previous post) get rid of the 18kw unit and replace it for a 3Kw to 5Kw, the his present cylinders could be used.
Personally I would push for option 1, rip it all out and do it again
As desirable as it may be to rip it all out (18kw is a lot for this application), It may not be in the budget to go to that expense. I think the tanks can be retrofitted to act as storage tanks without the HX and at least he can salvage the basic equipment. If he has room, he may be able to add one more tank if need be.