An 014, you can throw unloading out, both compressors will be can recips. Either 1 or both compressors or nothing in between.
Carrier did have an option on those units called a moisturemiser.
Basically they called it a subcooling coil which was placed on the leaving side of the evap and took hot gas off the compressor instead of using the regular air cooled condenser to reheat the leaving air and reduce humidity without using electric strips to do the job. You may look to see if the units could be equipped with that option and field install it. Control would be by humidistat and bring unit on in reheat mode running 1 compressor and auxilliary condenser, if set up right you could put airflow back to original.
You could still run wide open straight AC when the load hits in the summer. Probably similar to the RAWL device but designed for the unit by the manufacturer.
Mike Hopkins