Got a problem on a VRV RXYQ8P7W1B (unused), i've made the commissioning 7 days ago. The system failed to E4 the first night after ( low pressure detection by pressure sensor).
I recovered the refrigerant and found the good amount ( total=9.53kg ).
In the meantime i tested the pressure sensor reliability compared to my low pressure gauge manifold and the service checker data. I made a complete vaccum during 3 hours and started again to check it in heating mode.
After the system reached the HP target (50°C), i found the discharge pressure slightly high : 112 to 115 °C with discharge step down control activation, there were ice just after the main EXV output to the heat exchanger (just at the beginning).
The system failed to E4 again the last night !!! don't know exactly why i'm getting bored by an unused system !
Maybe a matter of bad EXV or something like that, i got a data recording of the 2nd commissioning.
Need your kind advises please it's for a child care centre..