Re: Heat Pump Modification
Hi, no need to SHOUT ;)
1) Who says that they are the same size ?
2) Don't understand the question, heat pumps will normally work in both directions as standard.
Re: Heat Pump Modification
Evaporator extracts heat at a DT of 6 to 10 K and the condensors rejects this heat and the absorbed compressor power back with a DT of 15K back to the outside.
So the 15K is at least twice or 1.5 bigger then the 6K, so the condensor can be half the size of the evaporator .
Most condensors have a fin spacing half of that of the evaporator, so again a reason why the condensor is smaller.
And your instructors told you that condensors in general are bigger????:confused: