Help on superheat and subcooling
I am dealing with a one ton trane, R22 with a txv and I have a superheat of 35 and subcooling of 20.. My gauges are reading 200psi on the highside and 60psi on the lowside and the ambient temperature is 80, The compressor voltage draw is 243 and compressor amp draw is 4.7 what could be the problem? Help please..
Re: Help on superheat and subcooling
If the ambiant temperature is 27dgrC (80F) inside? than 4,1 bar suction is too low!
What are the suction line temperature, discharge line temp and liquid temp? What's the entering temp and leaving temp on both evaporator and condensor?
hvac student
Almost anything...Is it not working then?
A Trane what? Chiller? AirCon? Model?
Compressor FLC is what? Give us something to compare it with.
A full set of readings is required before a reasoned answer can be given.
A one ton trane with an exspansion valve should have a subcooling of about 10,
I'd Start there
WOW, how about that spelling
clip prince
and it's all his own work :D
I have two problems, the Key board and the fact that I use Farenhiet.. 10 Degrees F. subcooling (just to be clear)
yes, you should describe the malfunction clearly, tell us what the problem is.
clip prince
I'd Start there
10 apple's, oranges, ??? ......camels.:o
if you want help or go in a discussion, make understandable sentences,and keep in mind its a world wide forum were we have miles and kilometers,and pounds and kilogram. :confused:
Ice