AHU tripping on the control panel
Hi everyone
I have a ahu tripping on the control panel..... I reset it and start it up and it works fine for 15 mins or so then just trips again.... Any ideas? I suspect it to be the fam motor but it spins fine and seems weird how it takes 15 mins to trip.
Thanks dan
Re: AHU tripping on the control panel
Did you check the amp draw and does it fit the over load settings?
Running overcurrent or the overload is failing.
Monitor the running current, check that all ahu access doors are closed.
I havent checked the running current as i didnt have my testers on me at the time. I know all the protective devices are correct as its been there for years. All doors are closed. Would there be any reasons for the running current to suddenly increase when it's been running for a while?
I will check the draw and running current tomorrow.
does it have a fan speed contoller
danielc4514
:eek:
Overload devices goes weak with time, causing them to trip at lower currents than they are adjusted to and marked for.
Electrical cables and terminations looses continuity with old age.
Electrical motors get worn with age and change their characteristics.
Fan belts get worn and change the loadings on the motors.
Fan scrolls get blocked and change the loadings on the motor.
Fire dampers closes.
Good engineering practices dictates that running currents are verified and over load devices re-calibrated as part of routine maintenance.
But then again, we just assume that it is an over current device tripping... It might as well be a thermal cut out or a flow control device or...
:cool:
Would the high ambient be a cause? Is the condenser really clean? Higher head pressure results in higher running amps. Just something to check if its been ok up till last few days.
The Viking
:eek:
:cool:
Thanks for that, very informative:). So today i checked the running current and it was 7.8 amps and the protective device was set at 6, after listening carefully you can hear the bearings are going. New fan motor it is then.
Thanks all for taking time to help
Glad you've found it and thanks for letting us know.
Good work.
Just a thought or 2;
If it's a belt driven fan, also check your belt tension and the fan bearings.
Also check the pulleys. I've replaced a lot over the years that have got worn out, often to the point where putting tension on the belt causes the pulleys to literally chew it due to pinching.