Re: Daikon Ftk25jv1nb fault.
When it starts flashing press and hold the cancel button . Then keep pressing the cancel button untill you hear a long beep. This will be the fault code
Deano240
Please read item 4 in the original post.
If the fault won't reset with main power off then you need it checked, below is part of troubleshooting guide:
6.35 DC Voltage / Current Sensor
Abnormality
Remote
Controller
Display
H8
Method of
Malfunction
Detection
DC voltage or DC current sensor abnormality is
identified based on the compressor running frequency
and the input current.
Malfunction
Decision
Conditions
„ The compressor running frequency is above 52 Hz.
„ If the error repeats, the system is shut down.
„ Reset condition: Continuous run for about 60 minutes
without any other error
Supposed
Causes
„ Defective outdoor unit PCB
Troubleshooting
Replace the outdoor unit PCB.
Hi Guys, thank you for the responses.
Re the unit, as per point 3) in my original. To add a further bit of info. I switch off at mains and await 30 seconds then switch back on. I restart the unit and run the fault diagnosis on the remote controller - pressing CANCEL on time section - and I get a long beep on 00 code indicating all OK - IE no fault. However, if I continue to cycle through the list of fault codes, after a few minutes, the long beep comes on H8 as per my original. Shortly after that the unit will fail.
A further bit of info is: the system is 13 years old, is situated in a holiday home in Italy and it gets little use. Only 4 years ago, the outside PCB was replaced, at a cost of 700 euros and it would not have had more than 300 hours use since.
So you can appreciate my concern.
Thanks again in anticipation of your response.
Best Mick.
13 years old. Probably time for a new system
Brian_UK
Cheers Brian. Not that I needed to be told that though. I couldn't delete my post. I see it afterwards. But thank you