30XA0502----0249-PEE- Carrier air cooled chiller
Dear Sir,
i am facing High oil filter drop pressure, Oil pressure transducer, Economizer pressure transducer and water exchange temprature sensor swapped alarms in 30XA0502----0249-PEE- Carrier air cooled chiller.
What to do?
How many gallons oil required for MODEL NUMBER:06TSA186SJ1C ( Carlyle) compressor
Re: 30XA0502----0249-PEE- Carrier air cooled chiller
welcome to re. first make it clear , what is the alarm code?
http://dms.hvacpartners.com/docs/100...0f/30xa-1t.pdf
manual for chiller
page 61 for what type of oil, and how to top up- might be worth checking oil solonoid is open and oil filter isnt blocked/restricted
As shown in the Touch pilot display the following four alarms are showing,
1.Circuit-A High oil filter drop pressure.
2.Oil pressure transducer.
3.Economizer pressure transducer.
4.Water Exchanger temprature sensors swapped.
And also i found small leakage in the plug fuse which is located in Economizer pipe line back to compressor.
Dear Sir,
dear sir- please look at post 3, the 1st line is highlighted- its a link to the service manual
click where it says "http://dms.hvacpartners.com/docs/100...0f/30xa-1t.pdf"
Dear Sir - Thank you very much.