Climaveneta.
Does anyone have a service manual for a Climaveneta FOCS/LN 1942 chiller. (circa 2005)
I have a fault code "compressor anomaly" that does not appear in the literature. I have tried climaveneta website but I am going round in circles
Many thanks
G
Re: Climaveneta.
compressor anomaly is a fault that is connected to the input from the motor protection module,
there are three
oil level
motor temp
and high discharge temp/
your controller is a w3000 carel
if you mail me i will send you back a manual
good luck
Re: Climaveneta.
Thank you, my email address is loooney@sky.com
Re: Climaveneta.
Re: Climaveneta.
You should ckeck the black protection inside the electrical of the compressor .