ranco V series stats
Which of the ranco stats can be used on air temp by pig tailing a coil on the cap end, also is there a 1200mm cap version,? and which is the one that contacts the evap plate,? I used to know all this but it,s been a while since I done any domestics
Dev
Re: ranco V series stats
Fridge Thermostat: Ranco VF3,VL3: Universal
Ranco:
UNIVERSAL
Freezer/Ice cream cabinet: 'No signal'
Cold out -34c, Warm out -16.5c, Warm in -12c, capillary length 2000mm:
Fridge Thermostat: Ranco VS5,VL5: Universal
Ranco: Compares to Atea W6, Danfoss Kit 6 and Whirlpool WPLW6
UNIVERSAL
Freezers with signal:
Cold out -34c, Warm out -16.5c, Warm in -12c. Signal operation cuts in 5c above cut in. Capillary length 2000mm
Fridge Thermostat: Ranco VT3,VT93: Universal
Ranco:
UNIVERSAL
Fridge Freezers with extra long capillary:
Cold Out -26c, Warm Out -11c, Defrost Termination +3.5c* (*Constant cut in) Capillary Length 3000mm
Fridge Thermostat: Ranco VT9,VL9: Universal
Ranco: K59L1102002 K59 Compares to Atea W4, Danfoss Kit 3 and Whirlpool WPLW4
UNIVERSAL
Two door Fridge / freezers WITH automatic defrost:
Cold out -26c, Warm out -11c, Defrost termination +3.5c* (*constant cut in). Capillary length 1200mm
Fridge Thermostat: Ranco VT9R
Ranco:
UNIVERSAL
Fridge/freezers with auto defrost. Where the original thermostat has an internal heating restrictor.
Cold out -20c, Warm out -8c, Cold in +3.5c. Capillary length 1200mm
Fridge Thermostat: Ranco VTD9,VLD9: Universal
Ranco:
UNIVERSAL
Fridge/freezers with heat assisted defrost systems.
The VT9D operates in a similar way to the VT9, giving a defrost on every switching cycle. The control is fitted with a SPDT (Changeover) switch, enabling the defrost assistence to be switched on during the defrost period.
The temperature setting range is -25.5c to -14c with a constant cut in at +5c
Fridge Thermostat: Ranco VXO: Universal,Candy,Kelvinator
Ranco:
UNIVERSAL
Larder Fridges
CANDY
Fridge Freezers:
KELVINATOR
Fridge Freezers:
Larder fridges operates in a similar way to the VT9 thermostat giving a defrost on every cycle. However, the temperature range setting is higher than that of the VT9 in order to prevent over freezing of the cabinet:
Fridge Thermostat: - Ranco VC1 KIT
Ranco
Compressor refrigerator
Cold out –23C, Cold in-14C.40C, Warm in +20C Capollary length 1200mm
Fridge Thermostat: - Ranco VP4/VL4
Fridge "Push Button" Defrost Cold Out -25°C" Warm Out -10, 4°C" Warm In -4°C Defrost Termination +5, 5°C
Cheers but none of these cut out at an air temp of 0C or above even at the "high" setting of 1 on the dial
Devlin