Re: Copeland D6DDA27 OE AWM
The pipe loop is for optional oil cooler, the two caps on adaptor, the one facing camera is a schrader for service gauge the right hand cap in for MP55 attachment, leave sensor in place.
I agree with Magoo.
Should you need to remove the sensor you have to change the gasket between the oil pump and the compressor to close the pressure ports and fit in a plug.
By the way, I think changing the Sentronic+ is not a good idea.
According to Copeland specs you should use a MP54 with 120s delay to prevent nuisance trips.
The modern Sentronic adds up the time you have problems with the pressure and is much more reliable than Danfoss MP.
Hi Aramis
you are correct, but with a Vogt icemachine I would prefer to have a shorter time scale. the ice machine can turn nasty real quick, saturating back etc..
Magoo
Hi Magoo,
OK, It's not me who'll get the blisters...:)
Chillin4alivin
... is, this where the oil pump outlet pressure is measured from?
Many Thanks
Not just outlet. The sensor is connected to two ports that draw inlet and outlet oil pump pressure.
So you cannot simply remove the sensor.
Thanks very much for your input guys - I now have a drawing of the compressor from Emerson that shows an external oil cooler so now i understand the concept of the pipe loop. The Vogts Tube Ice Machine uses hot gas to harvest ice (roughly 3mins). This is when i experience oil problems at compressor - When it reverts to refrigeration mode the oil is returned to the sump from the oil separator. Normal oil level is then achieved after a couple of minutes. Will update with results for info.....thanks again
Chillin4alivin
This shouldn’t be.
Oil usually traps in the evaporator at the lowest suction pressure, reversing the cycle should bring all this oil back.
This means that either the outside coil is traping oil, or …
… or the oil separator is not connected correctly or the crankcase pressure is too high in the reverse cycle.
Could you send us a picture showing the compressor discharge valve and reversing valve and oil separator together and the high and low pressures just before the cycle starts and just after?
... oh! and observe what you see in the sight glass at cycle changes!
Right Guys....bit late with update but here goes!
Problem with the henry oil separator, this has now been changed and returning oil at satisfactory rate.
We had oil lying inside the evaporator tubes...this has now been drained and machine is now making full capacity ice. Customer now happy and Engineer delighted ALL IS GOOD!!
Yah...the when the plant was on defrost the discharge pressure should lower a lot which penalizes the oil separation and because the oil separator wasn't good enough then the hot gas+oil were directly to the evaporator/ice generator.
Its all about equilibrium:cool: