Hello everyone,
i have problem with my Trane chiller RTAC250 that is low evaporator Rfgt Temp - ct1
and sometimes the same compressor tripped by low suction Rfgt pressure - ct1.so what shall i do?
Hello everyone,
Hi Cool King
Ask an engineer to sort out the problem
R's chillerman
you should takeCM 's advice!
this problem is something a tech that is qualified will be able yo deal with .
good luck
good evening,
these massages appaer as alarm so i think the unit needs more gas, is that right?
thanks
Evening Cool King
this does not have to be a refrigerant charge issue
it could quite as easily be a problem with part of the system
unless you can provide a full list of operating conditions
temperatures/pressures at various points
water temperature in/out confirm flow, correct vessel resistance
Its hard to give you an answer and really needs an engineer to attend to diagnose
R's chillerman
Hello ,
As per my experience , i have seen that mostly " low evaporator pressure " is due to low level of refrigerant in the chiller.In addition , there may be some problem in expansion valve.
Cool king , please provide us various parameters as chillerman said.
Have a good weekend.
I can think of at least 6 or 7 other things that will or could give the same fault.
In fact I have had to remove refrigerant charge from chillers maintained by very experianced engineers,who made the same assumption.
The advise being given is cautious for a reason, without the correct facts damage could occur.
Hi Grizzly
You had them too mate,
last one stuck flow switch, pumps not running(turned off der!)
and had to drag out over 22kg that had been dumped in
its quite amazing sometimes how dangerous a little bit of knowledge can be
& why do companies allow some to work on our kit...beats me
well with f-gas quals being so hard..things should improve :rolleyes:
R's chillerman
:D Thanks for the input chillerman.
Yep assuming can be humbling!
I prefer to say nowadays, "With what I know so far it would be a good starting point."
We all do it!
Chillers as you know have lots of reasons for displaying Low Suction or Temps.
Many times only because it's the first Fault parameter listed.
I hope coolking has not taken offence and keeps us all informed.
It would be interesting as what the actual cause of the alarms is.
Yeah me too mate
I was referring to ones who worked on kit prior to me
If he can start to list the conditions it wont take long to confirm whats going on
Just did not want him chucking in refrigerant if not needed
CoolKing we still here for you if we can help mate
R's chillerman
Hello everyone,
Operation conditions for TRANE chiller RTAC250 at different times:
at 8:00 am (SEP 27,2011)
Modes
chiller mode: Running
circuit 1 mode: Auto
cprsr1A mode: Auto
cprsr1B mode: stopped
circuit2 mode: Running
cprsr2A mode: Running
Chiller
Evap leaving water Temp: -7.2c
Evap Entering water Temp: -5.7c
Active chilled water setpoint:-7
outdoor air temp: 26.9c
compressor
1A
Amps L1 L2 L3 : 0.0 0.0 0.0
%RLA L1 L2 L3 : 0.0 0.0 0.0
unit volts : 418
oil Temp: 28.1c
Intermediate oil pressure: 127kpag
suction pressure: 124kpag
1B
Stopped Because comm. Loss: Starter 1B
2A
Amps L1 L2 L3: 120.0 115.0 113.0
% RLA L1 L2 L3: 62.6 58.5 55.5
Oil Temp: 58.9c
Intermediate oil pressure: 803kpag
Suction pressure: 104kpag
Rfgt ckt1 ckt2
Cond Rfgt pressure: 614 939 kpag
Sat cond Rfgt Temp: 27.3 41.0 C
Evap Rfgt pressure: 125 104 kpag
Sat Evap Rfgt Temp: -6.9 -9.4 C
Evap Approach Temp: …… 2.7 C
Rfgt liquid level: -8 -4 mm
at 10:50 am (SEP 27,2011)
Modes
circuit 1 mode: stopped by Low Evaporator Rfgt Temp-Ckt1 at 10:30AM
cprsr1A mode: Auto
cprsr1B mode: stopped (comm. Loss: Starter 1B)
Chiller
Evap leaving water Temp: -6.9c
Evap Entering water Temp: -5.3c
outdoor air temp: 29.2c
compressor
1A
unit volts : 415
oil Temp: 30.9c
Intermediate oil pressure: 116kpag
suction pressure: 113kpag
2A
Amps L1 L2 L3: 140.0 135.0 130.0
% RLA L1 L2 L3: 71.6 69.0 67.0
Oil Temp: 62.4c
Intermediate oil pressure: 933kpag
Suction pressure: 101kpag
Rfgt ckt1 ckt2
Cond Rfgt pressure: 669 1021 kpag
Sat cond Rfgt Temp: 29.9 43.3 C
Evap Rfgt pressure: 113 102 kpag
Sat Evap Rfgt Temp: -8.4 -9.7 C
Rfgt liquid level: -15 0 mm
at 12:04PM (SEP 27,2011)
Chiller
Evap leaving water Temp: -6.8c
Evap Entering water Temp: -4.9c
outdoor air temp: 28.7c
compressor
1A
Amps L1 L2 L3 : 68.0 64.0 61.0
%RLA L1 L2 L3 : 50.4 47.6 44.6
unit volts : 408
oil Temp: 32.7c
Intermediate oil pressure: 653kpag
suction pressure: 70kpag
2A
Amps L1 L2 L3: 141.0 135.0 129.0
% RLA L1 L2 L3: 71.6 68.5 66.2
Oil Temp: 62.1c
Intermediate oil pressure: 924kpag
Suction pressure: 105kpag
Rfgt ckt1 ckt2
Cond Rfgt pressure: 708 1009 kpag
Sat cond Rfgt Temp: 31.7 43.3 C
Evap Rfgt pressure: 110 105 kpag
Sat Evap Rfgt Temp: -8.7 -9.3 C
Evap Approach Temp: 1.8 2.5 C
Rfgt liquid level: 3 1 mm
at 12:13PM (SEP 27,2011) circuit 1
1A
unit volts : 410
oil Temp: 51.3c
Intermediate oil pressure: 50kpag
suction pressure: 48kpag
1A at 12:18 PM
%RLA L1 L2 L3 : 50.5 48.0 44.5
unit volts : 411
oil Temp: 58.1c
Intermediate oil pressure: 676kpag
suction pressure: 69kpag
1A at 12:21 PM
Amps L1 L2 L3 : 67.0 64.0 61.0
%RLA L1 L2 L3 : 50.3 47.5 44.5
unit volts : 411
oil Temp: 60.6c
Intermediate oil pressure: 651kpag
1A at 12:22 PM
%RLA L1 L2 L3 : 50.8 47.5 44.0
unit volts : 404
oil Temp: 61.3c
Intermediate oil pressure: 680kpag
suction pressure: 131kpag
at 2:57 PM (SEP 27,2011)
Modes
circuit 1 mode: stopped by Low Evaporator Rfgt Temp-Ckt1 at 12:41 PM
cprsr1A mode: Auto
Chiller
Evap leaving water Temp: -6.7c
Evap Entering water Temp: -5.2c
outdoor air temp: 28.9c
compressor
1A
unit volts : 407
oil Temp: 32.3c
Intermediate oil pressure: 132kpag
suction pressure: 129kpag
2A
Amps L1 L2 L3: 138.0 134.0 129.0
% RLA L1 L2 L3: 70.2 68.2 65.5
Oil Temp: 61.2c
Intermediate oil pressure: 916kpag
Rfgt ckt1 ckt2
Cond Rfgt pressure: 666 1017 kpag
Sat cond Rfgt Temp: 29.9 43.6 C
Evap Rfgt pressure: 127 104 kpag
Sat Evap Rfgt Temp: -6.7 -9.5 C
Evap Approach Temp: …… 2.8 C
Rfgt liquid level: -8 -1 mm
Hi CoolKing
lets see if we can diagnose this for you
All the readings need to be taken manualy and not off the controller
Need to know what refrigerant first ?
Then allow chilled water temperature to rise enough to call for compressor to run at full load 100%
Now at full load (no saturated temperatures - actual real temperatures)
List the answers to these conditions below
Water or Air cooled condensor
If air cooled - air on & air off
If water cooled - water in & water out
Ambient temperature
Discharge pressure
Discharge temperature
Condensor outlet temperature
Liquid line temperature (after the drier)
Suction pressure
Suction temperature
Evaporator temps/pressure taken through binda point
Water in
Water out
Water return pressure
Water flow pressure
R's chillerman
could you give me the complete model of the machine? if it's 250TR has two circuits each circuit with a compressor.
you need an engineer there simple
long list of possible problems. refrigerant is the last thing you want to look at and one of the most expensive.
no one can actually help without you having the right tools, besides fgas rules
Hi serviceman,
The machine is Air Cooled Series RTM Helical-Rotary Liquid Chiller, Model RTAC250, Fluid R134a, with two circuits first one has two compressors 1A,1B. Second one has one compressor 2A.
our problem with the first circuit that is compressor 1B stop by Comm loss: starter 1B and this is ok because we are waiting for STARTER MODULE for this compressor. But compressor 1A trips by Low Evaporator Rfgt Temp-Ckt1 and sometimes by Low suction Rfgt pressure-Ckt1.
please let me know For further information
COOL KING:
The Starter Module did not receive a transition complete signal in the designated time from its command to transition. The must hold time from the Starter Module transition command is 1 second. The Must trip time from the transition command is 6 seconds. Actual design is 2.5 seconds. This diagnostic is active only for Y-Delta, Auto-Transformer, Primary Reactor, and X-Line Starters.
This is a specific starter test where 1M(1K1) is closed first and a check is made to ensure that there are no currents detected by the CT's. If currents are detected when only 1M is closed first at start, then one of the other contactors is shorted.
LOW TEMP EVAP.
(calculated from suction pressure transducer dropped below the Low Refrigerant Temperature Cutout Setpoint for 1125°F-sec with a 8°F-sec/sec max integral rate applied during circuit startup transient (or 4ºF-s/s if manifolded and only one cprsr running) while the circuit was running early in the circuit’s cycle. The minimum LRTC setpoint is -5°F (18.7 Psia) the point at which oil separates from the refrigerant. During the time that the trip integral is non zero, the unload solenoid(s) of the running compressors on the circuit, shall be energized continuously and the load solenoid shall be off. Normal load/unload operation will be resumed if the trip integral decays to zero by temps above the cutout setpoint. The integral is held nonvolatily though power down, is continuously calculated, and can decay during the circuit’s off cycle as conditions warrant.
LOW PRESS EVAP:
a. The Suction Refrigerant Pressure (or either of the compressor suction pressures) dropped below 10 Psia just prior to compressor start (after EXV preposition). b. The pressure fell below 16 Psia while running after the ignore time had expired, or fell below 10 Psia (or 5 Psia in sftw prior to Oct’02) before the ignore time had expired. The ignore time is function of outdoor air temperature. Note: Part b. is identical to Low Evaporator Refrigerant Temperature diagnostic except for the trip integral and trip point settings.
QUESTION:
have changed the initial charge of oil?