hi all,
i have an o6e recip running full load.
77 amps fla
running 52 amps
suction 270 kpa
Discharge 1800 kpa
sst 8.5 C
sct 49 C
liquid pipe temp - 39 C
Suction Pipe Temp - 21 C
Running on 3 x TXV
Air on evap - 26 C
Air off Evsap 23 C
condenser 18 k split
Need to be seeing 10 k split over evap.
Used to get it but another tech attended site, gas leak and now i cannot trim the charge correctly very frustrating any ideas?