We need access codes to the carrier 30gx tell my please
I need access code service factorry 11 is not nebodet
could you eleborate on your last post
Carrier 30GX Can not DELETE OvErridE Chiller not starts, please If there SPITSIALISTY Who is to disassemble, please HELP
have you got an error code on the pro dialog control?
no error code, and does not start, which can be
how to enter service configuration
help me please
The service and factory access codes are for Carriers own service technicians and not for general release.
What else is the display telling you besides "override".
only shows the "override".
water in the ice water circuit? operate water pumps?, closed circuit switch water flow?. compressors are enabled? the configuration of the machine is correct? have some control or manually operated?
I've tried it does not work
what type of panel you have? comfortlink, navigator, pilot touch
I need access code for the test
panel pro-dialog+
that is not who does not know the access code
help me please :-)
level 1 2222
level 2 3333
Hi mail me and i will send u the manual ,this should guide u to solve your problem ,i hope your eprom wasnt erased!!
gill@gosheneng.co.il:)
I need a code to enter service configuration
11 is the code yusera, who was unfaithful to him I need a service code
Hi why dont u do as i proposed and mail me i will give u the manual .
this will help u !!!;)
I sent to your mail
please check mail
there is the idea
Alo people
Hi dont forget your time isnt most pepoles time and some work !!
4.5.7.2 - Password
A password must be entered in order to access the test function
or to modify a configuration. It is automatically requested, if
necessary: 'EntEr PASS' is displayed on the 4-digit display and
the configuration menu LED flashes, indicating that the
modifi-cation mode is active. Press the arrow keys until the
value '11' is displayed on the 4-digit display. Press Enter to
validate this. The configuration menu LED stops flashing. If
the password is correct, 'Good' is displayed. If the password is
incorrect, 'PASS incorrEct' is displayed. The User password has
a default value of 11.
This value can be modified through the Service configuration.
The password can be entered if the unit is fully stopped, otherwise
'ACCES dEniEd' (access denied) will be displayed on the
4-digit display. The controller automatically deactivates the
password after 5 minutes without activity (i.e. no buttons
pressed) or after powering up.
you can try 88 if that dosent work , i will speek to my carrier guy here and try to get the code :D
Code 88 is not podhodet
I have 4 digit display
I can not enter [SErviCE] [MAStEr SLAvE]
Are you running 2 chillers as master / slave.
and have 1 chiller configured as master control and the slave chiller is configured as CCN control.
The french pro -dialog chiller don't use a 4 digit service password.
Are the chillers started and stopped via a BMS or are they stand alone running 24/7
mistake I have 2 digit
and silence
what excatly is you problem??
is unit working??
change the unit to local mode and see if this helps