Quote:
Originally posted by fridgetech
There would normally be a large liquid mass in the evap at the end of a cycle, more so if the low load operation was lengthy before the pump down, then too there'd be a large oil mass in the evap.
If the controls are configured for non interupt pump down then there can often be multiple pump down recycles before the suction settles below LP cut-in.
Often these days one would introduce an interupted pump down controls configuration and then at the next start up have a pump down start-up with a LP switch timed overide.
Let me be the gadfly here, but mostly during the first pumpdown you have relieved the system of liquid floodback worries. That is when the large flooding issue is resolved. After that it is repeated starting and stopping for no good end. Having the cut-in pressure as high as practible is a good idea, though.