Quote:
Originally posted by Prof Sporlan
When evacuating a system from the low side, the TEV will open up, regardless if it has an MOP-type charge or not. The problem is the TEV, even when wide open, is a very small orifice for refrigerant to flow thru. As superheat says, it will take some time the evacuate a system this way. Standard procedure is to evacuate from both the high and low sides when access valves are available.
Well, I agree on that, but the volume inside the piping on the high side is not large. We are talking about a system which is orders of magnitude smaller than what most of you work with from day to day.