Re: oil compressor problem
Do a pump down test to check if your discharge valves are OK
Mr. Frank I make pump down it's ok
I have one eqution it's normaly go with ***** small quntity of oil , is that right
On a small system you should not need to add additional oil to the amount recommended by the compressor manufacturer.
On larger systems it is normal to add additional oil to compensate for the oil that moves around the system.
Ok, I have to tell you more information in this circuit there is no oil sapreater. Is it necessary to install oil sapreter
It depends on the size of the system
Hi Alamda.
I would suggest that the abnormal (I assume the amount of oil being dumped system side is abnormal?) oil carry over is very likely to be the result of wear internally within the compressor.
The Rings, Valves and Springs are a good place to start.
These comps are usually highly reliable, so ever mechanical wear or failure would be a good assumption.
When a recip has worn piston rings and liners (or even broken rings) they become a very efficient oil pump!
When you had the heads off did you check the sump for debris or metallic particles within the oil.
An oil sample analysis may prove useful.
Some recips have bypass valves within the head / liners, if relevant this could have an issue?
Good luck Grizzly
Does your system short cycle? If so, check out this link.
http://lvhvac.com/cope_bulletins/17-1262.pdf
passandscore
An interesting article there passandscore thanks.
I think Franks comment is all the more relevant having read it!
Plus add a working crankcase heater and Oil Foaming is minimised.
frank
can you tell me what is the size of the system needs to add oil seprator?
lose of oil have a lots reason.
rings
valve plates
high temp. of oil
oil type
foaming of oil in starting time.
wrong piping slop in suction line also u trap
blocking oil return from oil separator
mbc
lose of oil have a lots reason. rings valve plates high temp. of oil oil type foaming of oil in starting time. wrong piping slop in suction line also u trap blocking oil return from oil separator
please can u help me what is the resons of foaming of oil in starting time & How to solve this problem ? And the normal temperature of oil ?