Originally Posted by
nike123
These pressures and temperatures marked red does not have sense to me.
Where did you take that "discharge" pressure
Also, how did you calculated that negative subcooling temperature?
Give us all readings and where on system did you took them.
Also, you said that unit is "cutting out", but you did not say at what alarm (high pressure, low pressure, high discharge temperature, etc....) it is happening.
136-98=38 PSI
looks to me like pressure drop at evaporator (outdoor unit if it is split type) and belonging piping and maybe some kink on these pipes.